GE IC693CMM311 Manual or Modbus map
plumbo
Feb 2018
Sacramento
I have a 90-30 system with a ic693cmm311. Documentation is sparse, and based on a lot of googling, it looks like this card may have been used to communicate with a quickpanel. I still am not sure of this though. Client is not using the quickpanel anymore, it's sitting unplugged. The cmm311 is configured as rtu only - does this offer any hints as to the function of the cmm311 for this application?
I'm looking for documentation for the cmm311 that would tell me about what registers correspond to the modbus registers if the cmm311 allows the 90-30 to be a modbus slave.
Thanks!
The CMM311 is a serial communications module. It must reside in the same rack as the CPU module. It is not compatible with the CPU311, CPU313, 0r CPU323.
Modbus 400000 = %R0001
Modbus 300000 = %AI001
Modbus 100000 = %I0001
Modbus 000000 - %Q0001
Fairly certain we're allowed to share these and they're legacy at this point, someone please update me if not so, but here is the Serial Communications manual for the 90-30 Series PLCs. In it, you will find everything there is to know on the CMM311 module.
http://ucc.colorado.edu/fanuc/gfk0582d.pdf
If you have trouble viewing, contact me and I can find a way to send.
Thank you. I won't be able to test for a while, but I'll try to follow up
Good afternoon, GE FANUC IC693CMM311 PLC communication problem with the Win98 operating system program, have the BGM elite. already working in our...
4,941
Hello Guys, I'm working on Honeywell HC900. I am using the PID block. I have attached the Switch and loop block to it as well. I have attached a...
632
Hi, I'm assisting a friend remotely with a VFD he's planning on buying and looking for a manual before hand to start planning. It's a Vikye. The...
929
This may be a long shot, but would anyone have paperwork on the Nedap 3.5 KW Driver ( Ballast) UV lamp ballast Modbus can communicate with the...
367
Hello all, I have an old machine that utilizes two FEAC PC-116-24 controllers used for position monitoring and output to an OMORM CQM1 PLC. I did...
627