Hi I am a beginner to the GE PLC. I am working on a project to install two new viewmarq display. Has anyone ever connected or worked with this kind of hardware architecture, GE RX3i and View Marq Md4-0124t.
We have tried serial using CMM004 and Modbus TCO using ETM001. The display doesnt work, if someone has worked on such a scenario and can send examples would be highly appreciated. Thank You.
What protocols are available in the HMI? For serial you will have to configure the port in the CMM004 to match what the HMI uses. I'm pretty sure the CMM004 supports SNPX, which is probably what the HMI has available for GE serial. For Modbus TCP, I'm pretty sure you will need to set up a map in hardware configuration.
Viewmarq has rs-232, rs-485 and ethernet.
Those are not protocols. They are electrical standards.
I looked it up.
Modbus TCP Server or RTU Slave
and ASCII.
That's going to make things a bit more difficult. Normally the PLC is the server/slave and the HMI is the client/master. In this case, the PLC will have to initiate all exchanges with the View Marq instead of responding to requests for information.
You will need to set up COMREQ instructions in ladder logic. There are examples in GFK-2224 for the COMREQs to set up a Modbus TCP client.
I have a system using Rx3I CRU320 redundant CPU with Proficy Machine Edition Software. In the hardware configuration of each CPU module, under...
421
Hi Everyone, I'm in a maintenance team in a factory, I need to upload an existing PLC program for backup purposes. The existing PLC is...
1,495
1,172
Hi all, Given a variable VAR1 at an address of %R101 is it possible within the PLC program to decompose this so that you can say the address is of...
3,593
Is this possible? I want to read values from a power meter directly into my PLC. Is there any kind of documentation on how to set this up? My CPU...
6,397