We currently have done a few small projects using GE's RX3i and iFix SCADA using GE's Proficy Driver.
In the Rx3i PLC we need to publish any tags that are required in the SCADA as "External" so that they are accessible by Proficy Driver.
I was wondering what would be the downside to just publishing everything as External and then letting the Proficy Server (or any OPC server) just pick the tags that it needs as opposed to ONLY publishing a limited number of tags.
You will not notice any difference in either the PAC or the SCADA. Only those used take up band width, it may take a bit longer to validate to download the first time you do it. The PAC processor is fast enough to not notice the difference in all but the very largest of projects even then I doubt that it would make much of an impact.
Try it and let us know if you see any differences. :)
I have a system using Rx3I CRU320 redundant CPU with Proficy Machine Edition Software. In the hardware configuration of each CPU module, under...
421
Hi, we are using Rx3i CRU320 redundant PLC system and we noticed a discrepancy between Primary and Secondary controller. Couple of variables (DI)...
313
Hi there, I'm doing some extensive testing and commissioning with a slew of new Emerson PACSystems RX3i PLCs. It would be convenient to...
139
Hi there, Trying to get some ascii serial communications working via RS485 (COMMREQ functions). I have attached our wiring for the COM2...
1,002
Hello all, First time poster, long time viewer of these forums. Could not find my solution on here. We have had issues with a Comm Fail on an...
417