GE Versamax PLC Modbus communication
irshadhashim7
Jan 2017
Saudi
Hi All,
I am working with GE Versamax Micro 20 PLC on a project to read/write data from 2 Modbus slave devices. I have to read 3 different registers(420210,416600,416540) from Slave 1 and write 1 register(420210) to Slave1, also need to read 14 registers(adjacent registers) from Slave2 and write 28 registers(adjacent registers) to slave2. Since the address of Slave1 are not adjacent registers, Im using 3 COMREQ Function blocks for reading the data & 1 for writing the data. But registers of Slave2 are adjacent, so Im using 2 COMREQ functions 1 for reading and 1 for writing. Now the Modbus Reading/Writing takes too much time approximately more than 15 seconds to read/write a register. Can anyone help me to solve this issue??
Best regards,
Irshad
I would look at increasing the baud rate of the network to the highest common rate that all devices can be set.
Next, I would change the read registers in the PLC. Use some move commands to group the registers together, so they can be read in one command.
Hope this helps you out.
Regards,
Hi Garry,
The Baud rate is at its maximum. Versamax PLC supports maximum baud rate of 38400.
The memories of Slave 1 can't be changed, because Slave 1 is a VFD(Danfoss AQUA).
Slave 2 is ok, I changed to adjacent registers and using 2 COMREQ I can read & write data from/to slave 2
If you can't change the addresses you need to read, you're stuck with needing to perform six separate transactions. Three reads and one write with slave #1 and one read and one write with slave #2. If you are currently using timers to sequence the six COMREQ instructions that control the transactions, look into monitoring the status word of each COMREQ instructions and using it to trigger the next COMREQ.
Also, consider not executing the writes as frequently as the reads, especially if the data you are writing doesn't change very often.
Edit: I have no experience with that particular drive, but I have worked with several devices that support Modbus which allow you to customize an area of consecutive memory with whatever parameters you want. Check to see if Danfoss offers that option.
Hi Garry,
Im using IC200USB002 communication board for modbus port. And the next port is programming port. So, which port you are talking about? If it is Programming port, is it possible to make the port as modbus master? Because by default it is configured as SNP slave. Im afraid to change the configuration of programming port, because if anything happened I can't communicate with the plc right?
Depending on the firmware version of the Fc202 it supports function code 23 (17h) read/write multiple registers. Using that you only need one call for each slave.
You'll be very very lucky to find a master that can execute FC 23.
Yes, FC 23 is in the Modbus spec, but I'm struggling to remember if I've ever run across a master that implemented it.
I've only used Modbus with Modscan32 (and Comm Suite) and here it is supported.
I'm wondering why it has been implemented then, if no controllers can use it.
Ah, the mysteries of life ;-)
Anybody can help in this case< I want to connect Versamax PLC to RTU using modbus, can I use the exixting two ports RS232 or RS 485 to do this or...
3,909
Hi, The VersaMax PLC suddenly stop running (no LED on run function) so I'm trying to upload the program. The HMI connected to it says "Host...
135
Hi, I am trying to set the IP address on the IC200UEM001 Ethernet Option Module. I am following the procedure in the manual for setting a...
433
Hello! Our PLC stopped working.(Controller CPU hardware failure) What can we do? https://prnt.sc/txskqe
1,808
I'm trying to utilize a PLC that my employer already had on hand for a project. For the life of me, I can't figure out how to get my computer and...
5,214