Hi All,
I new to this GE VersaMax Profibus DP Slave.
I don't how to start it. How to do the configuration, mapping?
In this project was used CPU001 + IC200BEM002 + 32 Input Module + 16 Output Module.

I just need to share all the Input & Output signal from VersaMax CPU001 to the PC (SCADA).

Can anyone help me?
 
I already read this Manual GFK-1534.
But i still not understand how to define the address in the IC200BEM002 properties.
How to do the %I and %Q mapping with the addressing?
 
The configuration is done in the Hardware configuration portion of Proficy Machine Edition software for Remote I/O or one can use the 'defaults' as described in the manual.
The first Input is %I1 the second is %I2 etc. up to %I32
The first Output is %Q1 the second output is %Q2 and so on up to %Q16
Yours may begin at different address but they are sequential from first to last.
What else do you need to know?
 
Last edited:
I used 32 Input Points (%I1 - %I32) module and 16 Output points (%Q1 - %Q16)
At the proporties of IC200BEM002, the "Status Area Address" in "Settings Section" was shown "%I00001". At the "Input Data Area" --- Area Number = 1, Data Type= Byte, Length = 1, Reference Address = %I0001. At the "Output Data Area" --- Area Number = 1, Data Type = Byte, Length = 1, Reference Address = %Q0001.

There will some errors & warning shown up when do the Validate the program.
 
%I and %Q are usually used as bits not bytes.
What is the Error number? or just click it in the 'Feedback' window and view its definition in the 'Companion' window of Proficey ME.
 
The error as below shown:-

Error 8304: Fatal overlap %I00001 - %I00008 [Rack 0, Slot 1, Input Data Area:1:Reference Address:'%I00001 - %I00008']
Error 8304: Fatal overlap %I00001 - %I00016 [Rack 0, Slot 1, Settings:Status Area Address:'%I00001 - %I00016']
Warning 8400: Non-fatal overlap %Q00001 - %Q00016 [Rack 0, Slot 3, Settings:Reference Address:'%Q00001 - %Q00016']
Warning 8400: Non-fatal overlap %Q00001 - %Q00008 [Rack 0, Slot 1, Output Data Area:1:Reference Address:'%Q00001 - %Q00008']
Error 8300: Invalid configuration for IC200BEM002 module [Rack 0, Slot 1]
Exporting folder...
Validating block: _MAIN....
Warning 8022: Type mismatch between variable and instruction.
Building block: _MAIN....
Size of Logic Binary File = 237 Bytes
Successfully processed.

Validating Aborted - 3 error(s), 3 warning(s)
 
The error as below shown:-

Error 8304: Fatal overlap %I00001 - %I00008 [Rack 0, Slot 1, Input Data Area:1:Reference Address:'%I00001 - %I00008']
Error 8304: Fatal overlap %I00001 - %I00016 [Rack 0, Slot 1, Settings:Status Area Address:'%I00001 - %I00016']
Warning 8400: Non-fatal overlap %Q00001 - %Q00016 [Rack 0, Slot 3, Settings:Reference Address:'%Q00001 - %Q00016']
Warning 8400: Non-fatal overlap %Q00001 - %Q00008 [Rack 0, Slot 1, Output Data Area:1:Reference Address:'%Q00001 - %Q00008']
Error 8300: Invalid configuration for IC200BEM002 module [Rack 0, Slot 1]
Exporting folder...
Validating block: _MAIN....
Warning 8022: Type mismatch between variable and instruction.
Building block: _MAIN....
Size of Logic Binary File = 237 Bytes
Successfully processed.
Validating Aborted - 3 error(s), 3 warning(s)
These are from PME's online Help (To be efficient, you should spend a little time learning how to use PME.)
Error 8304:
Possible Solutions
If module configurations have overlapping reference address mappings, edit the module parameters to correct the overlap.

If the error is the result of a reference address overlap between a module and an EGD exchange, edit the reference address and/or length either for the module or for the EGD exchange.

If the error is the result of a symbolic variable or I/O variable overlap between a module and an EGD exchange, edit either the module or the EGD exchange.

If an offset in a consumed exchange is mapped to a function block input parameter, replace the parameter with a valid variable.

To enable input reference address overlaps, for example, when setting up redundancy modules, set the following HWC option to Warn: Input Reference Overlap. Use this setting with caution.


Error 8300
:

Possible Solutions
Configure the module parameters. For example, correct an invalid range entry or reference address overlap, or enter a valid number or block name.

If the error is the result of a reference address overlap between a module and an Ethernet Global Data (EGD) exchange, you can edit the reference address and/or length either for the module or for the EGD exchange.

Replace the module with itself.

Caution: You may need to reconfigure the module.
 
I also not so understand. If 1st slot is IC200BEM002, 2nd slot is Input Module (I0001-I00016) and 3rd slot is Output Module (Q0001 - Q00016). How do I configure the I/O seting in IC200BEM002 and how to do the I/O mapping between physical I/O with BEM002? I know how to use PME, but i don't understanding with the I/O address mapping in Profibus.
 
I also not so understand. If 1st slot is IC200BEM002, 2nd slot is Input Module (I0001-I00016) and 3rd slot is Output Module (Q0001 - Q00016). How do I configure the I/O seting in IC200BEM002 and how to do the I/O mapping between physical I/O with BEM002? I know how to use PME, but i don't understanding with the I/O address mapping in Profibus.
 
The system is trying to tell you that the CPU is using one or more of those addresses for something else. In the IC200BEM002 change the configuration of where the Profibus puts its first 2 bytes of Input data and Output data to a different Address. Once an address is selected that will work it will turn from "Red" to "Black" in the hardware configuration area.
Then you can program using those Addresses.
 
Proficy Machine Edition 7

Hey Friends ,
I have Site code F739-6020
Can anyone help me how to get Authorization Code ?
Thanks
 
hi steve bailey can you help me if what is the problem with my hardware config. IC695PBM300 pofibus to communicate to an GE Fanuc VersaMax Profibus Network Slave Module (IC200BEM002)
i will send to you my plc hardware config. via email
 

Similar Topics

I am building a new panel with a GE Versamax PLC and 6 ABB freqdrives, among other things. The powers that be have decided to control all 6 drives...
Replies
3
Views
5,861
Hello, Has anyone set up Profibus on a Ge Fanuc Versamax? I have looked some in the documentation but it would be nice with a white paper or...
Replies
0
Views
3,896
I have one GE Fanuc IC200PNS002-AC Versamax Network Interface Module and the fault red light is blinking and i have checked in manual it is...
Replies
9
Views
223
Hi, The VersaMax PLC suddenly stop running (no LED on run function) so I'm trying to upload the program. The HMI connected to it says "Host...
Replies
0
Views
139
I do have a problem with a GE Versamax micro PLC. By going online (on Port 1) the "OK led" goes down. Power led stays On Port 2 no reaction at...
Replies
4
Views
396
Back
Top Bottom