GSV question
KingPresident
Aug 2015
Michigan
138
Is there an attribute I can use with an input block to detect if an input has a proximity sensor plugged into any particular port, while the proximity sensor is not detecting, or not passing voltage?
If it’s is an io link sensor and an io link master then yes, otherwise I don’t believe so but depends on what you are using for the “block”.
It depends on the input module and the sensor.
Some diagnostic inputs can detect broken wires on the input, and have a "pulse test" feature.
A method that doesn't depend on the input module's technical features is to get a switch that has both a N.O. and N.C. output, and check them to be sure they are complementary. If both or OFF or both are ON, then something has gone wrong with the wiring or the switch.
Thanks. The obvious tips are difficult sometimes. Found what I needed in the manual for my equipment. My flavor of IO block has Channel Diagnosis.
Hi All, I just an issue with a 1756-enbt/a in a L61 remote rack. Was dropping comms randomly so i decided to replace the card as well as the...
1,288
I'm trying to dig to the source of a minor "recoverable" system fault throwing a fault light on a machine that has been confusing my operator...
98
So, I'm really just trying to get some experience by practicing with arrays. I'm using studio 5000 v33. I have one rung with an XIC bit that's...
243
Hello all, I know in the past it's been the case that we wanted to limit the total number of GSV calls per scan of the PLC. Is that still the...
664
Hello, I have a question regarding the status checking of the module in the secondary chassis in a redundancy setup. CHASSIS 1 ...
1,143