Control Logix GSV question

James42005

Member
Join Date
Dec 2018
Location
Waterloo, IA
Posts
35
Hi All, I just an issue with a 1756-enbt/a in a L61 remote rack. Was dropping comms randomly so i decided to replace the card as well as the cable. I want to monitor the status of this module since it is possible that the remote rack could lose communication and nobody realize it. However it could cause some major issue to our process if it does. I have used GSV's before to get PLC time and others things. My only question is how many elements of the destination DINT tag should I create?

Thanks,
 
One DINT.
GSV | Module | EntryStatus.
If it equals 16384 (0x4000, 0100 0000 0000 0000b), the module is running.

If it isn't running, you can get more information from:
GSV | Module | FaultInfo
 
Thanks, so it set it up as entry status. The value i return is 16896. With bit 9 and 14 being a 1 of my destination DINT. I believe i only want to see the bit 14 high. What is bit 9?
 

Similar Topics

Hello Members We have a controllogix redundancy setup and need to display the status of redundancy in panelview. I have found in the manual the...
Replies
8
Views
1,269
I am having trouble with getting no control of my analog output signal. I am using the SCL function block to control my analog output. The logic...
Replies
11
Views
261
hi all, i have a plc i need to get info from for a site im working on: I have a 1764 Micro Logix 1500 LSP Series C (See Attached Image) im...
Replies
2
Views
383
I currently have a weird issue involving Ethernet IP communication between a ABB CI873 (EthernetIP Module) and a 1756-L83ES. The Layout is as...
Replies
8
Views
767
Possible for two processors in same rack to have separate motion groups across a single Kinetix Rack using a single EN3TR? One 6500/5700 rack, 8...
Replies
1
Views
428
Back
Top Bottom