Hach Opc Tag Interace Software
plcengineer
Jan 2004
USA
176
I have implemented a HACH Process OPC Link software at a clients facility. The client has requested that we provide visual alarms with setpoints. The HACH software doesn't have this capability. Does anyone know of a software out there that would interface to the HACH OPC software? I need the software to provide a graphical interface and allow the operator to input alarm setpoints.
Thanks,
plcengineer
I too am trying to get up to speed on OPC for a project I am doing. Are you seeing data from your hardware in the OPC server? I have only used RSLinx for OPC and they have a utility to see if the data is getting in there.
There are a lot of HMI packages out there that read data from an OPC server and can provide alarms and setpoints. Intellution, RSView, Wonderware, Cimplicity, etc... They are expensive though.
I have seen smaller OIT's that have built in web servers that I believe can read in OPC data and have alarming capabilities. I think it was from Advantech, and with their software was amazingly inexpensive.
I contacted Hach and bought a kit they recommended for a customer to add Modbus TCP capability to his Chlorine Analyzer with a SC4500 controller...
237
Usually I go to Hach with these problems but they are being slow to respond and sending me Italian emails...? RSLogix 5000 - 1769 L32E PLC...
1,517
Hi all, Client called saying that the turbidity readout on the HMI is 0.0000 but on the local readout, it shows an actual value. Sure enough...
5,421
Hi all, One of my clients has a Hach sc200 measuring Nitrates (wastewater plant) and the 4-20mA loop works, but the local readout is just...
1,368
Hi all, Recently a client had an issue with their Hach sc100 and while I got the instrument back up and running, the analog outputs for the two...
1,579