HARDY load cell controller to QUANTUM
karivelm
Nov 2006
Quebec
66
Does anybody know what material I will need on the PLC side to communicate with a Hardy controller ?
Hardy says Ethernet/IP, Modbus TCP, Devicenet & Profibus are supported with a HI-4050 controller.
The PLC this will be connected to is a Quantum 140-CPU-213-04 on a modbus plus network...
Will I need to use a special communication card in the QUANTUM to get the communication going ?
Since the Hardy doesn't list ModbusPlus, you have some other options:
an 140NOE771 xx will do ModbusTCP
an 140NOC771 01 will do Ethernet/IP and Modbus/TCP
My personal preference is ethernet, and ModbusTCP is simpler than Ethernet/IP, so I would buy an NOE and ethernet switch (prefer managed switch here) and go that route. There are other ways to solve this problem, but this is what I would do.
I will have two of these systems, so I guess 1 140-NOE771-11 card will do... I will connect it to a switch and then connect to each of my HI-4050 controllers?
Do you have any idea where I can get info to know how to interface between this card and the controler...(Programming - How do I send and get info from the controler)
Yes. This sounds right - but two systems... is that two Hardy controllers connected to one PLC (one NOE), or are they separate PLC/Hardy systems, in which case you will need two NOEs, one for each system.
The NOE documentation is on the Schneider Electric website. Without looking at the Hardy controller documentation, I would start with IOScanning on the the NOE to the Hardy devices. There are other ways to do it, but this requires no PLC code, just some configuration.
Did you check the Hardy website for documentation? They have to have a table of Modbus registers somewhere and what they contain... so you know what to enter in the NOE.
1. Setup the network with IP addresses and such
2. Look up the information you want from the Hardy controller and find what the IP address is and what registers contain that information.
3. Enter the information from (2) in the IOscanner table
The data then just 'appears' at the PLC registers you setup. Works pretty well.
This isn't much detail, but if you find the information I described we can get more specific about what goes where.
Hello, I have a set of three tanks with their own trio of Hardy 6600 series load cells. Two of them have no issues with where they are at and...
156
Hi 3 Cells connected to a summing board, then to the series b hardy weigh module then connected to device network. Can not calibrate the cells...
2,586
Does anyone have any idea when the Micro850 will be coming out? The last note I saw on it on this forum was from June of last year.
3,876
Does Any one have a program for Logix 5000 for this card. the one from Hardy is not that great and is a little hard to follow. Thanks for any...
2,331
Hello I am trying to configure a hardy 1769-ws scale card for a micro logix 1500 and the manual is tuff to understand does anyone have a better...
1,880