Hart Converter
Depends on what you mean by a HART system. What defines it as a HART system?
A. Do the analog inputs have a HART modem that reads one or more HART variables?
B. Does the HART AI act as a passthrough for an asset management system to use HART to configure the field devices?
C. Are the HART devices on a HART multiplexor?
D. Are the HART devices all on HART multidrop network with HART master that polls them one at a time?
E. None of the above but the field devices can be configured and troubleshooting done by a HART communicator of some sort?
There is no device that 'adds' HART to a non-HART device. So if that's what you're looking for try, solicit an opinion from someone who is less straightforward than I am.
Situation A: Your non-HART device's 4-20mA will work on a HART enabled AI but your device will not provide any HART data, only the 4-20mA signal.
Situation B: Your non-HART device will work on a HART enabled AI but without HART the asset management software can not talk to the device.
Situation C: Your non-HART device's 4-20mA signal will generally work with HART multiplexor but again, no HART data is available, only the 4-20mA signal
Situation D: Your non-HART device will not operate at all on a HART Multidrop network.
Situation E: Your non-HART device will work as well as any non-HART device with a 4-20mA output, but of course, it can't be configured with a HART communicator.
I am going to need to use HART multi-drop in order to handle a series of Vega Radar units. There are a lot of options and I'm wondering what...
281
I'm not actually in front of the equipment yet, but this is the information that I have been given by a client: ------------ Data from HART...
352
Just started working with some HART loops and I'm trying out Pactware.I'm using Krohne and it works just fine recognizing my modem. I downloaded...
1,461
I have a field device (flowmeter) using HART wired to a 200SP HART input card. I need to read flow totalization. Configuring the actual card to...
666
Good Afternoon All, I'm trying to read a totalizer from a McCrometer flow meter into a 1769-L33ER processor via a 1769sc-IF4IH hart module...
896