HC900 Modbus TCP anomaly reading
For increase the counter limit i can also use a second counter for count the addition factor (counter 1 + (counter 2 * 1000000) ) for example.
It's enoght 12 hours for compare ther registers ? On HCD i can see every addition, every step but on the client i see the value registered 12 our before.
Can you see in the image the value of the counter ? In the client i can see a value always lower (how is possible when on HSC i see that blocks run ad the value increased).
Ennio
SOLVED
It was difficult receive a information from Honeywell support, but they send me a trace to find the solution.
The customer can't stop HC900 to set the correct order byte (Big/Little endian).
So with the client modbus and another modbus tool we started to try the right byte order and ther right address because with a shift of -2 from manual, we intercepted probably the mantissa of float register with a CDAB order.
The solution is a ABCD byte order and a shift of -1 from manual to find the right value in modbus register.
Ennio
Thank you to everybody
You don't have to stop the processor to change the Modbus TCP Double Register format.
Also, I'm surprised that the Client doesn't have the capability to adapt without touching the processor.
If you are "shifting from the manual" then you are working around an issue in the client not the processor. The manual is very thorough in providing information regarding how it handles Modbus Registers.
I'm glad that you are satisfied with your solution, but I want anyone who follows this thread to know that there are (4) word\byte order options available in the HC900 for situations where the client is not flexible enough to use the HC900's default. The manual for the HC900 is very good at providing both the Decimal and Hexadecimal Registers and you have the ability to build your own maps as well.
Hey everyone, Im kinda of stuck in a situation and Im asking everyone support on this please, I truly need everyone help. Here is the situation...
602
I am currently working on a steam generation plant. We are using Honeywell HC900 C70 controller. There are 30+ instruments connected to E&H...
2,865
Hello everyone. Using the designer software for the HC900 had me thinking. How can I assign 1 variable so 1 single bit. Like how can I say that...
449
hi all i test the HC900 modbus (master) read function by connecting s1 port to my notebook with rs485 usb converter. in the HCD, i monitor the...
4,173
I'm upgrading an existing machine with a Honeywell HC900 controller, and I'm trying to do some data processing in the controller. I have variables...
56