Heat/Cool PID block
Old No. 7
Jun 2010
Ohio
173
I'm working on a project with a Micrologix 1400 with a temperature control PID block. The system has both heating and cooling, but the tricky part is that the cooling is not always enabled. What we have done in the past is rescale the PID so that when cooling is disabled 0-100% is heating and when cooling is disabled 0-50% is cooling and 50%-100% is heating. I'm not sure this is the best way to approach it and was thinking about having two PID blocks. One for heating and one for cooling. Anyone have any experience with this type of setup?
A lot depends on whether you are cooling above ambient temperature. Normally cooling isn't required above ambient because the system will eventually cool to ambient anyway. Obviously you need to cool below ambient. Cooling above ambient is optional.
You should have different gains for heating and cooling. If you have two PIDs then each can have its own gain. Then it should be easy to switch between the two depending on whether you are heating or cooling.
I would use two PIDs if you need to use cooling.
A little more info.
The system is batch processing in the 1700 F range. Sometimes at the end of the batch, the furnace is cooled to 1550 F. What typically happens is the cooling is enabled to get the furnace and load down to 1550 F and then the heating comes back on to hold at that temperature.
We usually have the same gains for heating and cooling, since cooling doesn't do much control. Once it has cooled to setpoint, the heating takes over. We do have to double the gain when we enable cooling so the system output acts the same when it is scaled 50-100% instead of 0-100%.
Heat/Cool – First Experience Although we have extensive PID heating experience for thermoplastic injection molding, today we are faced with a...
2,111
Hello all! I am fairly new to the world of PLC's and this forum, so I apologize for my lack of knowledge. I have a Powerflex 753 that keeps...
584
Hey All, I've got a Vacon x4 VFD running in open-vector mode. It is spinning a heavy pin-mill wheel. It gets frequency reference from a PID...
20
2,564
Hi Can someone please tell me where I can find information about the heat developent / dissipation of a Simoreg DC Master? 📚 The information...
943
Hello all, Some of you may be familiar with the RAM searching program for Windows computers, Cheat Engine. You can search RAM directly for...
749