Hi everybody,


I'm new to Rockwell/Allen Bradley and need some help here.


The client has 4 SLC5/04 CPUs in the plant, all in a DH+ bus and connected to a RSView32 SCADA computer (PCI Card, DH+ Bus).


I need to connect a cMT-SVR100 to these PLCs, but none of them has ethernet connection and cMT-SVR supports both DF1 and DH485 but NOT DH+ (Ouch!).


Is there any way I can do that?
Maybe can I get the data out of RSView32 and send it to the cMT-SVR? How?



Thank you very much!!
 
Just took a look at the product brochure:
https://dl.weintek.com/public/cMT/eng/Brochure/cMT_Brochure_ENG.pdf

Am I wrong in that the only way to connect this HMI to a PLC is via OPC UA ?
Rockwell RSLinx can be an OPC UA server, so that could be a way.
What I dont like about that is that it requires a PC which if turned off, you also lose the connection between the PLCs and the Weintek HMI.
 
Am I wrong in that the only way to connect this HMI to a PLC is via OPC UA ?


You can connect this HMI to PLCs directly. I've already done that with Siemens, Schneider and OMRON PLCs. It can also comunicate with AB PLCs via Ethernet, DF1 or DH485 (DB9 port).


Rockwell RSLinx can be an OPC UA server, so that could be a way.
What I dont like about that is that it requires a PC which if turned off, you also lose the connection between the PLCs and the Weintek HMI.


I don't like the PC dependency, but that solution, at least, is a proposition to be made. How can that be done? I'm absolutely new to AB and RSLinx
 
Hi welcome to the forum! Attached is a way to use RSLinx as an OPC Server. It shows one how to do that using Linx and Excel, but perhaps it will help you along enough to configure it as a server to your other equipment. This was posted by another person a few years back and I copied it for future reference. Hope this helps.
 
Hi welcome to the forum! Attached is a way to use RSLinx as an OPC Server. It shows one how to do that using Linx and Excel, but perhaps it will help you along enough to configure it as a server to your other equipment. This was posted by another person a few years back and I copied it for future reference. Hope this helps.


Thank you! I'll check that
 
Does the HMI support using a DH+ gateway? A 1756-ENBT and 1756-DHRIO in a 4 slot rack will allow you to connect to a DH+ network via Ethernet using standard CIP protocols.
 

Similar Topics

A few weeks ago while walking through the back part of our plant an coworker and I found an old GE Versamax Micro PLC (IC200UDR005-BB) on the...
Replies
13
Views
2,486
Please help me in configuring my PLC and Internet setting. I have uploaded system architecture, please check out. Thank guys.,.,:(
Replies
0
Views
1,170
help in communicating GX Developer(Fx1N) with Citect scada 7.20--- serial communication.
Replies
10
Views
4,225
hi everyone, my problem is that whenever i try to view accessible nodes or try to download the object files into my plc, it generates differnt...
Replies
13
Views
2,520
hi everyone, my problem is that whenever i try to view accessible nodes or try to download the object files into my plc, it generates differnt...
Replies
0
Views
1,380
Back
Top Bottom