Help: Connecting PLC to existing BACnet system
Forrest
Dec 2009
Vancouver
45
We have a new project to setup a control panel with PLC DL205. This PLC should be able to communicate to the existing system with BACnet protocol. Actually, this is my first project to setup communication for BACnet protocol. Can someone tell me what I need to consider. I searched from the web and found that we can buy a hardware BACnet driver. Connect this hardware driver to PLC and then setup point mapping file to this BACnet driver, then our system can communicate to existing devices using BACnet protocol. Is it right?
Thank
Sorry, do you mean that the link between our PLC and BACnet driver? Actually, I am not sure how to link my PLC to BACnet driver. I also need to check it. Any suggestion?
By the way, after checking with Google I see this unit series provides Modbud to BACnet conversion. The DL205 (I would recomment the DL260 CPU) can speak Modbus RTU directly from the CPU or Modbus/TCP from an ECOM 100 Ethernet module.
Thanks bernie,
We are going to use FieldServer BACnet drivers but it seems that there is no driver supporting DL205. Am I right?
I also found that there are some MODBUS to BACnet convertors on the web. If you used the convertors before, may I have your suggestion on the model so that I can check and see how can I use them
The DL205 uses Modbus RTU via RS-232. You would need a Modbus RTU driver and the appropriate BACnet driver (MS/TP or IP, likely) programmed into the FieldServer. This would be a very easy conversion. You would just need to know how to place the data in the proper registers within the DL205.
Not to knock that Sunlux product as I have never worked with it, but the Red Lion DataStation Plus product could also be the nice go between the BACnet and Modbus comms.
Joe_WaZoo
Finally, we decided to use DL205 (CPU260) with MODBUS RTU D2-DCM, connect MODBUS RTU to FieldServer QuickServer MODBUS to BACnet, and then program the map file for FieldServer. Hope it works! (this is my first time to program BACnet)
Hi, I have a Micrologix 1400 with a 1762-IQ16 discrete input module, wired for sinking inputs (common to DC-) I have an instrument with the...
12,764
Hello, I am working on a line where we use a Siemens PLC S-300 and where machines from others company are using either Siemens or Telemecanique...
1,605
Hi. I am working on a project where the customer has inquired if it is possible to connect a barcode-reader to the plc to make the setting of...
2,545
Hello i need help, I've two momentum plcs with the processor 171CCC98030-IEC and i need to put the 1º plc to read and write registers in the...
3,343
I don't get it. I belive i'm configuring correctly the PLC to power ON/OFF and control the speed set point of the Masterdrive yet I get an error...
4,468