Help on Micrologix1500 Error
jim-garcia
Oct 2003
Reynosa
42
Hello all
I try to set a value into analog output from 0 -10V
using the scp on verify file show not errors
but at verify project show the next error
Operand sizes did not match
here is my scp parameters
SCP
Input N7:0
input min 0
input max 100
scaled min -32768
scaled max 32768
output O:3.0
thank you all for your time
If the Analog Output is configured for 0-10 VDC then the SCP operand Scaled Min should be 0 and Scaled Max should be 32767.
What analog card do you have? Complete catalog number please.
How do you have the card configured? ( which data data format are you using?
Post your .RSS file if you can. ( zip it first)
The upper range is 32767 not 32768. But the upper range for 10V depends on the card and how you have it configured.
Error Help on micrologix 1500
thank you
here is a copy of my code
does the n7:0 can be used instead of an analog input ?
one more time thank you all for your help
Yes you can use N7:0 in the SCP instruction.
See picture below, take note of the count values for a 0-10 volt output from your card.
You will need to change the scaled min/max to get 0-10 volts output.
-29788 = 0 volts
+29788 = 10 volts.
help on micrologix 1500
-29788 = 0 volts
+29788 = 10 volts.
hi thank you for comments
one more thing when I try to run the CPU it go to error
say the module vendor not identified
any Idea
thank you for your time
jim
any Idea
jim
Here a knowledgebase article that might have something in there. I don't have a tech connect contract to view it. If you do take a look or maybe someone who does can look.
20289 - Processor I/O fault for 1769-OF2, 1769-OF8C, 1769-OF8V, 1769-OF4CI and 1769-OF4VI Modules
This document is based on the following assumptions: The module will be correctly connected to any CompactLogix or MicroLogix 1500 controller. Modules include: 1769-OF2 1769-OF8C 1769-OF8V 1769-OF4CI...
Access Level: TechConnect
Created: 10/03/2001
Updated: 01/11/2013
I skimmed through that article and don't think it applies to this fault.
I think the first thing I'd try and reconfiguring the I/O config of the project and making sure my I/O module was connected correctly.
Never did it myself either...I have used 1762 expansion hardware on ML1200s but never 1769 on ML1500s...
The 1769 Analog Modules do not have a 16 bit resolution when used on "partitions" of the full Min/Max range; that's where the +/- 29788 raw values come from for a 1769-OF8V; the 16-bit resolution (+/- 32767) is used to detect "under/over Range" conditions.
Okay so I just went into my ML1500 and mistakenly changed a comm setting for channel 0 or 1 channel config section of the programming software...
1,176
this a program to send data to barcode printer I want to integrate a new printer in a new machine and i wanted to adapt the old prgram on it but I...
76
50
Hi all, hope you are having a great day, I am in need of your help to create a AOI or program that does this kind of job: I have a IO Link...
24
420
please help me . I have to make this ladder diagram and I can’t figure it out :(
359