I am a student. Please share on the right wiring of the attached PLC (Panasonic Nais FP1-C40. I am using AC connection and able to power ON the PLC but not able to turn on the input.
I am using photoelectric NPN sensors as input. Do i need to ground all the Com input and connect the sensor output with 24V? (As illustrated in attached files).
Your help is much appreciated.
Thank You & Best Regards,
Benita
Hi Benita,
Have a look at the manual in the first link provided by osmanmom, page 46 (PDF page 54), there's an example there (as always... read the manual first!). basically your inputs can be made to be either sinking or sourcing just by changing the common voltage applied to the COM terminals. When the common voltage is 0V, applying 24V will turn the input on. When the common voltage is 24V, tying the input to 0V will turn the input on.
This second option (24V applied to COM terminals) is what you want to. then you connect the emitter leg of your sensor to 0V, and the collector leg to the associated PLC input terminal. Sketch it out and post back and i'll let you know if it's right.
Some PLCs only have sinking inputs, i.e. you have to apply 24V to the input, and the common is internally tied to 0V. In this case I normally use a pull up resistor which is connected to +24V on one end, and the NPN sensor terminal AND the input on the other end. that does require you to invert the logic in the code, as when the sensor is OFF then the input sees 24V, i.e. on.
http://web.encoder.com/Portals/146177/images/Pull Up Circuit.JPG
But you dont need to do that, because yours can work both ways.
Hi Benita,
Dear Saffa,
Please help me by provide a rough sketch. Much appreciated.
The sketch JRB had provided will work for you.
Mind you, this stuff is all very clear in the manual. If you hope to be successful in the automation world, then you need to learn. .. RTFM.
( Read The F$@#king Manual )
Good luck!
It Works!
Dear Saffa, JRB & Osmanmom,
It works..Appreciate your reply on this.
It realy works, thanks alot for the guidance.
Kind Regards,
Benita
Hi, I'm new to this Forum. Can anybody help me with following. I want to reprogram an old Matsushita (Panasonic) NAiS FP3 PLC. CPU model no...
3,133
trying to find a store front I can go to in hopes of purchasing an programming cable for Panasonic PLC. The cable part number i have is FP0-PWS...
6,091
I have a NAIS FP1-C40 that has been pulled from storage after many years. Needless to say that the battery is dead, no program. I called the OEM...
16,599
Good morning all: I have programmed extensively with many AB packages, many Omron packages, Idec, TI, but never Nais. I'm using FPWin Pro4. I'm...
3,450
Hello, I am trying to work with a nais fpo-c14rs and am using FPWIN PRO 5. I have slowly worked through the "on disc tutorial", and have problems...
4,131