Help with Beckhoff terminals
kallileo
Jun 2008
Thessaloniki, Macedonia, Hellas
353
I have a Beckhoff CX7000 IPC with some digital I/O built-in and I additionally need two analog inputs 0-10V.
Can I install both Ethernet terminals (EL3062) and the older K-type bus terminals (KL3062) on this IPC?
The CX7000 is E-Bus or K-Bus sensing. Depending on which card you plug in immediately after the controller it will sense if it needs to be in K-bus or E-bus mode.
If you choose the first terminal as K-bus all subsequent terminals to the right must also be K bus type (KL, etc)
If you choose E-Bus (EL terminals) then you can place all of your EL terminals.
You can in fact go from E-Bus to K-bus on a rack, you place all the EL terminals, then you need a BK1250 (compact coupler between E-Bus and K-Bus).
Once the the rack is converted with the BK1250 to K-bus all subsequent terminals on that rack must be K-bus. This is meant to allow you to use E-Bus cards for the higher performance or functions only present on EL terminals, while still utilizing some of the K-Bus stuff (slower IO, Special Function cards) basically allow you to reuse any k-bus terminals you might have.
Info on BK1250 [ HERE ]
Patrick
Any help for a Beckhoff PLC that does not start up correctly the first time? The system will lock up, stop responding at times, requiring me to...
1,770
Dose anyone have experience with Beckhoff FC3121 profibus master PCIe card connected to Siemens CP342-5 as a profibus slave? The data retrieved...
17
4,806
Hi, I have received a copy of a PLC program for a customers Carton erector that uses a beckhoff PLC and HMI. I just downloaded the trial version...
2,269
Hello, so I guess I'll start by saying I didn't design this system, or even am responsible for it's maintenance... just trying to help out and...
2,041
Ok working on TwinCat for first real time. I cannot seem to find a way to do a compare in the ladder. The way our driver works (from our...
28
13,844