Windrunner
Hello everyone,
I'm having trouble selecting the right circuit breakers for the "line side" of my VFD. The common advice is to check the manufacturer's recommendations. While the manual suggests specific in-house types, I'm unsure about alternatives. Also, I don't need UL certification.
My VFD is a PowerFlex4M (22F-D2P5N113 series A), and the manual recommends:
Fuse: UL Class J, RK1, T, or Type BS88; 600V (550V) or equivalent.Circuit Breakers: HMCP or Bulletin 140M, or equivalent.
I'm having difficulty finding suitable alternative parts or determining what the equivalent part might be.
Additionally, can I use an MCB instead of an MCCB or MPCB? For example, on one occasion when we used an ABB VFD, one of the options mentioned in its manual for selecting the supply disconnecting device (disconnecting means) was: a circuit breaker suitable for isolation in accordance with EN 60947-2. In that case, we simply used the following MCB (Miniature Circuit Breaker): Acti9 iC60H, 3P, 6A, B curve, 10000A (IEC/EN 60898-1), 15kA (IEC/EN 60947-2).
Or am I interpreting it incorrectly, and the option mentioned above does not pertain to the characteristics of the CB but rather to its capability to be placed in the OFF position and safely disconnect power?
Thank you.