Hey All, I’ve got a problem for anyone experienced with SLC5/04s running on DH+ controlled by a windows 98 desktop running Wintelligent View.
So I’ll try and provide as much information as possible but I am not at all fluent with these older systems. We have an aggregate processing plant that was set up ages ago, as far as I can tell it is 3 SLC5/04s running off of a DH+ network in a BUS network, my coworker removed the processors in an effort to set them in a set of racks we had lying around to set up a test scenario so we could figure out what the controls on the PC do to the files in the programs on each, since we have ZERO documentation. (he has the idea of using a panelview plus 15” connected with a RTAENI-N34-D realtime Ethernet interface card.) however it didn’t work, for obvious reasons because the test racks were not identical to the racks we pulled out and did not have matching input and output cards. He hooked them up and all he did was click “Clear faults” and didn’t change anything from there on out. The problem lies in that we have put the processors back in their original racks, and now something has broken communications between the HMI and the processors, (see attached pictures.) any help with this would be greatly appreciated!
This is the error I get when starting WintelligentView
but I have communication between the 3 processors, as seen here.
and I can view the data tables of each processor
Also if this Is a completely futile endeavor, and it would be a better option to rip the 3 SLCs out and upgrade to a compactlogix with Point I/O, please feel free to voice your opinions on that too, as that was my opinion.
I would be more concerned with the W98 running RSView32 more than the SLC's
With everything powered up have you rebooted the PC? or restarted RSView? I remember one project that has a few slow to boot nodes so I had to boot the RSView PC last after a complete power loss to the plant
Yeah, we tried rebooting everything several times in different successions, including PC last. Here are 3 screens I am not sure will be helpful or not.
Each picture is of the status of a different processor.
UPDATE: got them working by changing processors to program mode then back to remote and power cycling. I noticed they were stuck in program mode on that diagnostic screen. Now the question is, what is the most effective way to figure out what each button on this HMI changes. Any suggestions?
You will need someone with more knowledge in WW then I have, if you post the SLC program there maybe an easy was if its documented
Hi everybody, I'm new to Rockwell/Allen Bradley and need some help here. The client has 4 SLC5/04 CPUs in the plant, all in a DH+ bus and...
1,707
Hi Guys, I need some help with a machine that has an SLC 5/04 communicating with a wonderware panel over DH485. I can monitor the logic while the...
3,338
I'm having an issue getting online with a PLC SLC 5/05 on the network. I have gone online with other processors over Ethernet but these are giving...
1,958
im using Slc5/04 one of its 8 channel analog output module 1746-NO8I got defective if i replace it with new one do i have to re-program or...
3,265
I have some old customer equipment. A PanelView 900 color (2711-T10C9) which has a DH485 Sub D connector communicating with a SLC 5/05 via its...
1,423