Cheers, I have contacted Mcc Automation, they will send me a price on Monday morning.RS have them in stock; http://uk.rs-online.com/web/p/plc-a...24F5448267573743D313736312D63626C2D706D303226
Ignore the picture it is "representative of range" not the actual cable itself...
Yes for analog you will need analog sensors as well as the input module. Cheapest is going to be temperature, then level, then conductivity. An industrial conductivity sensor, from the likes of Endress and Hauser, is going to be above £1.2k. Your level sensor will need to be capable of withstanding the caustic solution. Your temp sensor you will get away with a PT100 with a RTD-4-20mA transducer.
This is the kind of stuff that has me swamped, would I be right in saying that most industrial standard level probes give an current or voltage analog output? I might see if there is any better way of measuring the tank level.Car fuel tanks have a float attached to an arm which wipes over a resitive strip. You will need to check the analog input manual to see if it can take a resistive input, it may be only 4-20mA or 0-10v in which case it may still be possible but you will have a bit more work to do.
Yea I need to spend some time and look in to all of this. I'm only planning to use a very low concentration level. What do you work at yourself?Yes, industry standard is 0-10V or 4-20mA. In my opinion for your situation the best may be non contact, i.e. an ultrasonic sensor mounted at the top of the tank. Assuming your tank is cylindrical, then volume = P*R^2*H, Height being given by the ultrasonic sensor.
Or you can try get a cheap pressure transducer, mounted at the bottom of the tank, every metre of water gives (off the top of my head IIRC) 100mBar of pressure. But the contact sensor may not like your caustic! And the ultrasonic sensor may not like if your tank is enclosed causing a "caustic cloud" at the top when you start heating...
Very good, this course should be not bother to you soCurrently a systems engineer in the automotive industry, maufacturing of sensors (Pressure, level, etc). Previously 7 years in the dairy industry, working with caustic in CIP (clean in place) systems.
Hi George, Its 1764-28BXB, it requires the 9pin Din to the 8 pin mini din. I should hopefully be able to get one sorted next week.Just another possibility on the programming cable...
Which ML1500 processor do you have?
1764-LSP - RS-232 8-pin port on base unit only
Or...
1764-LSP - RS-232 9-pin port on left side + the above
If you have an LRP processor then you use a 1747-CP3 cable. This is a null modem cable, so if you happened to already have one you would be good to go.
Either way, it's always good to have a 1761-CBL-PM02 knocking around.
Geospark said:Just another possibility on the programming cable...
Which ML1500 processor do you have?
1764-LSP - RS-232 8-pin port on base unit only
Or...
1764-LRP - RS-232 9-pin port on left side + the above
If you have an LRP processor then you use a 1747-CP3 cable. This is a null modem cable, so if you happened to already have one you would be good to go.
Either way, it's always good to have a 1761-CBL-PM02 knocking around.
Hi George, ah I see what you mean when it comes to different part numbers for the base unit and the controller. Mine doesn't have the isolated RS232 comms port, so my controller is a 1764-LSP.Sorry, slight typo error on the above!
Padraic,
You're quoting the base unit catalog number. One or the other of the above catalog number processors are plugged into that base. If you are not seeing a 9-pin port on the left side then you have a 1764-LSP processor and will need the 1761-CBL-PM02.
One more small detail. The 8-pin port is not an isolated port whereas the 9-pin is, if you have that model. You are advised to use an isolating device between an un-isolated port and your PC, but many don't bother, I'm sure. A typical isolating interface is the 1761-NET-AIC+.
G.
Nice to see another fellow Paddy about the place. There's not enough of us here at all....
Padraic said:Is it recommended to have an isolated connection? Is the idea to prevent damage to the controller?
If I use a 1761-NET-AIC+, will I need a 9 pin to 9 pin?
Mickey said:Your source for cables...http://www.plccable.com/communication-cables/