HMI and SCADA Process Value not corresponding
IdealDan
May 2017
MA
480
Hi Friends,
A quick one please:
What could cause HMI and SCADA Process value/data NOT corresponding?
A temperature value having up to 5 degree Celsius difference between the HMI (Panel View Plus) and SCADA (Vijeo Citect SCADA).
PLC is CompactLogix
Ethernet Network Communication.
Your inputs are immensely appreciated.
Regards
Hi Friends,
A quick one please:
PLC is CompactLogix
Regards
Is this a new tag? Has it ever been correct? What datatype?
The first thought that comes to mind is, as others here have posted, - "a HMI should be a window into the PLC."
My thought is that either the HMI or SCADA is doing some internal calculations, maybe adding a temperature offset value to compensate for an off reading, that got fixed when a thermocouple was replaced but the offset was never removed. I ALWAYS do these things in the PLC.
Are you sure the SCADA and the HMI are reading the same tag? I wouldn't say that it's common practice, but where I am at the moment, the developers were so poor at creating a SCADA system that it's common to see what effectively should be the same value being different because it's linked to different places in the PLC.
Failing that, and I've never used Vijeo, some SCADA packages have the option of mapping values to ranges. This isn't common on real values, but it's one potential source.
the first thought that comes to mind is, as others here have posted, - "a hmi should be a window into the plc."
my thought is that either the hmi or scada is doing some internal calculations, maybe adding a temperature offset value to compensate for an off reading, that got fixed when a thermocouple was replaced but the offset was never removed. I always do these things in the plc.
+1
I think there is a tendency here.
yes, they are reading the same Tag
After an online change to a PLC, a HMI can be left subscribing to the old addresses of the tags. I think there is protocol to solve this, but there was a time when not everyone had implemented this.
Rebooting the HMI could solve it.
My instinct would be though there's a configuration difference. Calibration values, filters on the tags, different tag, different PLC etc.
Hello, I'm working on a machine retrofit project, and am looking for recommendations for HMI/SCADA software. I've used C-More and Horner HMIs...
1,943
We currently use GMail accounts for sending email alarms from quite a few HMI projects. Specifically C-More HMIs and AVEVA Edge runtimes. To...
7,559
  • Poll
Am I old school? Now networks are getting vey fast are you directly addressing tags in the PLC or do you create a dedicated HMI/Scada memory area...
3,362
Hi guys, I want program a aggregate Scada/HMI, i read the manual but i didn't understand well. Does any one know how to get a value from the...
1,988
Hi Everyone: Has anyone used "FAS-inMOVE Operation & Monitoring – Visualization" from INRAY INDUSTRIE SOFTWARE ?. Any experience, any comment...
1,484