HMI/Controller Page Request Function - Help Needed

zstair

Member
Join Date
Nov 2009
Location
Harleysville, PA
Posts
2
I have a Baldor MintDriveII controller w/motor and a KPD-TS10C-20 Touchscreen HMI with a "Panel Controller Interface" setup screen where I can "RDA Setup" by checking the "PLC" checkbox and the "PR" (Page Request) check box and stating the COMMS38 as the location it is stored.

I have not been able to use this page request function to move any screen pages on the HMI. I write a value to COMMS49. PageRequest = COMMS49 (declared variable), where COMMS38 = PageRequest. I have a "refresh" Task running that should refresh the values as the HMI writes to COMMS49.

I am writing 10000 to the comms38 as I have been told there is a 1/1000 scaling to try and set PR to 10 to have the HMI screen change to page 10.

Help. Please. -zack
 
So after a few months wondering, I put a post on here and low and behold its because I should be writing to COMMSRAW38 instead of COMMS38.

Genious!

Have Fun - Zack
 

Similar Topics

I am trying to get a Mitsubishi GT2715 HMI to read and write from a Eurotherm 3508 controller using 4 Wire RS485 Mobus RTU communications. The...
Replies
3
Views
1,313
Hello friends, I’ve recently started learning about PLCs and HMIs after I acquired a Wago 750-871 with one digital input card and two digital...
Replies
20
Views
5,619
Hello all, we are trying to connect STM 32 microcontroller to Proface ( GP 4301TM) HMI via Ethernet. Currently another microprocessor board is...
Replies
11
Views
4,050
We have robot - Fanuc make RJ3IB controller in our r and d cell.and we would like to have an external HMI connected to it. Through HMI we want to...
Replies
2
Views
1,656
How is the boot time on the PANELVIEW 800 HMI 2711R-T4T? I am familiar with the old Panel View Component AB 2711C-T4T and the boot time of over a...
Replies
15
Views
6,432
Back
Top Bottom