HMI Panelview Plus 7 Firmware Version

rngtech

Member
Join Date
Jul 2022
Location
London, England
Posts
11
Hi all,

I'm still learning so apologies for silly questions.

I have developed a HMI runtime on Factorytalk View Studio V13.00. I have gone to download it to the Panelview Plus 7, but get the error that the firmware is only V12.0. I have gone onto the Rockwell website but see that V12 is the latest for the PV+ standard. Am I missing something here or will I need to copy my V13 application into a V12 application?

Thanks
 
When you make the runtime, you need to change the target version to v12. So Application > Create Runtime Application, Save Type As: Runtime 12.0 Application (*.mer)
 