Honeywell Multitrend SX Modbus Master help
PLBoudette
Jan 2006
Albany, NY
41
I've got a Honeywell Multitrend SX paperless recorder that I'm using as a Modbus Master device to poll another I/O device for some analog inputs it contains. Everything seems to be working. I've tested the slave device with a Modbus master simulator and hooked it up to the Multitrend. The LED's and the recorder show successful communication. I want to make the new analog input data into pens on the chart. However, I don't know where to retrieve the data in the recorder. I've scoured the manual and internet to try to find a solution. Anyone know how to solve this? Thanks in advance.
Pete
Yeah, I've done that. Page 87 (pdf) from the recorder manual:
Each slave can perform up to 8 “transactions”,
where a transaction can retrieve or send 1 or more registers from a slave, or retreive
or send 1 or more Pens to a slave. Access to slave registers within the maths function
has been provided using SCV (Slave Comms Variable). For example SCV[x,y,z], where x =
Slave number, y = Transaction Number, and z is the each successive register retrieved​
starting from 1 (Item).
Hence, the pen 'math' statement = SCV[x,y,z]
I seem to recall that the SCV x, y, and z terms are defined in the Modbus master transaction setup at completion of the setup, although the z term might not be individual, but for a range of values, like 1-11 or something like that, so you'd use 1 for the first, 2 for the second, etc.
There's an example on the app sheets, where connection to another Honeywell device is described, one for Modbus RTU over RS-485
http://hpsweb.honeywell.com/NR/rdonlyres/8A10B2E0-41AA-4475-94C8-F830DAD5881E/61411/43TV3397.pdf
another for Modbus TCP,
http://hpsweb.honeywell.com/NR/rdonlyres/982E2285-54C6-40C5-9FF1-B146CD580EB8/61401/43TV3392.pdf
but the way the data is used in a Trendview 'pen' is identical for both and applicable to any Modbus slave device.
Dan
This is more of a knowledge base post as opposed to a question. Hopefully somebody can learn from my issue. We've recently installed a Honeywell...
1,966
I am trying to use the scripting functions in a Honeywell Multitrend SX to set digital outputs based on digital input status. Scripting is...
1,973
So...we bought this equipment to use it specifically for TUS (temperature uniformity survey). We ran test surveys from 30 mins to 180 mins...
3,182
Got locked out of the setup. Need an administrator to unlock the user account but its the administrator account thats locked. No way to get back...
5,356
Hi Anybody knows how to enter Honeywell HMI config menu. I need to change date and time of HMI. HMI series: Honeywell HCi series
111