Honeywell s9000
shaun croman
Oct 2003
carlisle
36
I want to connect 2 OPC servers to a honeywell s9000 but because it only uses one port for communications it keeps crashing the system.
So I want to bridge the connection between the honewells and OPC servers...
Does anyone know of any device that I can use to do this?
I have to ask: I assume that you need two OPC servers because you have two different OPC clients each of which need the S9000 data.
Why can't your OPC server serve two OPC clients?
If I recall properly the S9000 uses the serial Modbus RTU protocol. Serial Modbus RTU does not tolerate multiple master queries.
There might be a possibility of using a serial server configured as a bridge to convert from Modbus RTU (serial) to Modbus TCP (over ethernet).
Modbus TCP can handle multiple Modbus Masters.
I've used boxes like Lantronix Xpress DR-IAP to convert Modbus RTU to Modbus TCP successfully for a single Modbus TCP Master.
Dan
The OPC servers are on a pair of redundant servers which run in tandem so each one will need to see the honeywell to provide proper redundancy- I have used this for years on one of my sites that uses Bradley PLC's which don't seem to suffer the same way (OK they are a bit more modern as well!)
The honeywells currently communicate over ethernet- meant to mention this before
Hey guys, I am trying to pull the ladder logic out of some ancient Honeywell S9000 PLCs, but I can't find the software anywhere (google search...
4,894
Hi, does anyone have any experience using ModbusRTU on an S9000 series Honeywell controller? I have multiple 9100e controllers that I would like...
2,973
I'm having some seemingly random ethernet faults on a Honeywell s9000. What happens is that the ethernet card goes offline and the LPM has to be...
4,070
Hi Anybody knows how to enter Honeywell HMI config menu. I need to change date and time of HMI. HMI series: Honeywell HCi series
116
Hi all. Would anyone happen to have the Modbus register datasheet for the Honeywell/EnergyICT EIMFlex Modular Meter v1.11 We've 40 of these that...
71