How do i get message on hmi when PLC looses power
Laker31
Apr 2014
sault ste marie
I am working on a senior project. I would like to have either an Alarm or a message on the HMI saying that the PLC lost power or the communication was lost between the HMI and the PLC. I have read somewhere I could use the timeout from the HMI. However I do not know how to configure it or where to find it. Please help me.
I use the following equipment:
- AB PanelView Plus 1000
- FactoryTalk View Studion - Machine Edition
- AB Compact Guard Logix L45s
- RSLogix 5000
Thank you,
Ta Da! Task complete
- RSLogix 5000
Thank you,
When you panelview displays "Error" in 100% of you objects that have a PLC tag connection...... then you know that the HMI is not connected to the PLC.
Welcome to the Forum ! Have the snowbanks melted yet up in the Soo ?
RSLinx Enterprise has a pre-defined Item called "@IsPresent" for each Shortcut. It tells you if the communications path to the controller is running.
You can use it as an Alarm Trigger, or to animate the Visibility of some warning text.
The syntax is just [ShortcutName]@IsPresent
Thank you Ken.
Unfortunately there is still snow bank in the Soo and I was not able to make your advise work. When I write your syntax in the visibility expression for my warning text it tells me that i have an invalid character in the expression.
Here is screen print of it. http://imgur.com/ZCJP6oa
Thanks for your help
Shame on me for not checking. The curly brackets go around the whole thing.
I think that's because an RSLinx Enterprise pre-defined Item is more like a Direct Reference than it is like an HMI Tag, because it explicitly includes the Shortcut.
{[TeamLOCI]@IsPresent}
Ahh, I've never used @IsPresent before so I though it was special in that you didn't have to bracket it. Hopefully that works.
G.
Thank you everyone, the text box appears now.
However, it takes 20 s for the HMI to realize that it lost communication with the PLC controller. Is there anyway to make the HMI reacts faster?
I don't think there's a way to configure the timeout.
I think 20 seconds is far too long for a fast network, but it's probably set way down at the TCP/IP stack level and those sort of long timeouts are traditional.
I found this...
43438 - @IsPresent is slow to change when the Ethernet cable is pulled
Access Level: TechConnect
Seems it is configurable Ken?
G.
Both RSLinx Classic and RSLinx Enterprise have an @IsPresent pre-defined item.
That technote refers to adjusting the timeout in RSLinx Classic.
As far as I can tell, there is no similar method for adjusting the RSLinx Enterprise drivers that the PanelView Plus uses.
Why not simply read a square wave heartbeat pulse from the PLC and trigger an alarm via two counters in HMI logic that increment whenever Heartbeat==On or Heartbeat==Off? That would verify not only a good communication link, but that the PLC is actually running.
I often use variable increment to indicate PLC heartbeat. When it goes to 0, I know there's something wrong either with the PLC or communication in between.
I was trying to connect an HMI and a LED MEssage Display Screen to my PLC. My PLC has two serial port supporting Modbus. Unfortunately one of the...
2,396
Hello guys, PLC - Omron CJ1G-CPU44H Ethernet module - CJ1W-ETN21 IP address - 192.168.10.11 Proface HMI(1) - GP2500S IP address - 192.168.10.51...
3,788
hi everyone, i have problem regarding Audit in FTV ver 12,In audit message "service disruption:<HMI server name>:<SERVICE NAME>" message logged,i...
50
Siemens S7/TIA v16: "Overwrite if object exists online?" HMI loading message... Thus far, I've just been ticking this box, just to get the HMI...
776
so im not sure if what i have come up with is the proper way to accomplish what im looking to do so hopefully someone here can straighten me out...
3,528