How to configure a 1769-IF8

pdk2008

Member
Join Date
Apr 2008
Location
Rocky Ridge, MD
Posts
4
I am trying to add an input to a 1769-IF8 which is being read by a CompactLogix L35E. I want to add a 4 to 20 ma signal into input 3 and have entered 8000h into configuration word 20 and 0203h into word 21, but still the input gives me a zero through out the input range. Any advice?
 
pdk2008 said:
I am trying to add an input to a 1769-IF8 which is being read by a CompactLogix L35E. I want to add a 4 to 20 ma signal into input 3 and have entered 8000h into configuration word 20 and 0203h into word 21, but still the input gives me a zero through out the input range. Any advice?

configure the card in the I/O tree


1769_if8.jpg
 
Make sure that you have a JSR pointing to the routine that you have the input programmed to or it will never execute. That has gotten me before.
 
Thanks for the advise. I found my solution. In RSLogix 5000 controller tag, Local:e:C, e is the slot number, I needed to be offline before entering my configuration numbers, then the program needed to be re-downloaded.
 

Similar Topics

I have installed 1769 IF4 analog input module in compact logix rack slot 3. I have an existing 1769 8 channel input card in slot 2 already...
Replies
2
Views
2,466
Hi All I've read the manual...didnt understand much... I have a accurate flow meter that gives pulses with certain width. just have to obtain...
Replies
6
Views
3,014
Hi folks. I have a system that I'm working on that needs 2 alarms banners with different event subscription: - One banner for a specific area...
Replies
6
Views
215
hi all i am new here i have a mitsubishi smart touch hmi i.e ms-60t-pe but i cannot find a software to edit and download a program in it any help...
Replies
3
Views
188
Hello, I am trying to connect a Stride Analog Output module to a 1769 CompactLogix via Ethernet. I added a new Generic Ethernet Module for the...
Replies
4
Views
269
Back
Top Bottom