How to connect an ET200SP in Logix Designer over Ethernet?

dolbeau

Member
Join Date
Jul 2019
Location
Knowhere
Posts
2
Brand new to Allen-Bradley. Trying to connect a Simatic ET 200SP to an Allen-Bradley plc and can't figure out the device configuration. It does not exist in the module type list so I assume it needs to be a generic ethernet module. If that's the case, how do I determine the comm format and connection parameters? If not, what should I be doing instead?

Using:
Studio 5000 Logix Designer V31.00.00
Simatic ET 200SP IM 155-6PN ST
 
Really obvious question here, but does the IM 155-6PN ST actually support EIP? Siemens IO usually just has ProfiNet (PN, like your part number) and ProfiBus (DP) options.


There was a third party collaboration IM (from SST, i think?) that you could use on ET200S, though.


Lots of the Siemens drives support EIP, the HMIs do, other stuff like RFID does, but the core automation components? Not usually.
 
Could be that it isn't supported. The manual that I found doesn't mention EIP. In that case I would need a gateway like those offered by anybus and prosoft, correct? Any recommendations?
 

Similar Topics

Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
Replies
0
Views
58
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
337
I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
121
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
Replies
2
Views
151
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
368
Back
Top Bottom