With RSLogix5000, how do I detect a com fail on a Ethernet VFD?
I usually use Ethernet to talk to another PLC where I'll program a heartbeat signal on both ends. With the VFD, (I'm not using implicit messaging) it just sits in my IO tree and I poll the input and outpu assembly instances. Is there a way to "pick off" the yellow triangles?
You wouldn't. If you just want to use messaging to the Micrologix it doesn't need to appear here. Just like a display isn't entered in the I/O tree. Only units that the Control/CompactLogix will automatically interrogate for I/O data are included in this.
Don't put any PLC-5, SLC-5/05, or MicroLogix controller into the Ethernet I/O tree of a ControlLogix family controller.
They don't support Produced/Consumed Tags or slave I/O connections, and the attempts by the ControlLogix to establish one can interfere with the normal operation of the PLC/SLC/MicroLogix network port.