Hi everyone,
Got some big problems here and I could use some help.
I have a system that is using a 1769-L33ER along with 3 remote I/O Racks. 2 are 1734-AENTR Point I/O remote rack and one is a 1769-ANETR remote rack.
For HMI's I am using 2 Red Lion G308 and 1 Red Lion G09.
Here is my situation: Today the processor went into a major fault. It was a I/O fault that caused it. That was no big deal except that the HMI's all continued to show good tank levels. I assume that was the level when the controller went into a fault. So the tank levels showed good even though the levels were climbing, eventually overfilling.
I have a tag in the HMI's for IsDeviceOnline but that alarm never showed up so the Processor must have been responding to request.
I know that since the PLC was faulted it wasn't scanning the values for a change so that is why the HMI was stuck on a value that was "reasonable".
So how would you go about getting some kind of alarm on the HMI to let people know that the data they are looking at could be wrong?? Or how do I go about making forcing the tank levels to a really high value in the event of a Major Fault?
I need to find a way to try and keep this from happening again! I have other plans in place to also help but I cant have the HMI showing good data if the PLC isn't even working properly.
Thanks so much for any and all help!!
Got some big problems here and I could use some help.
I have a system that is using a 1769-L33ER along with 3 remote I/O Racks. 2 are 1734-AENTR Point I/O remote rack and one is a 1769-ANETR remote rack.
For HMI's I am using 2 Red Lion G308 and 1 Red Lion G09.
Here is my situation: Today the processor went into a major fault. It was a I/O fault that caused it. That was no big deal except that the HMI's all continued to show good tank levels. I assume that was the level when the controller went into a fault. So the tank levels showed good even though the levels were climbing, eventually overfilling.
I have a tag in the HMI's for IsDeviceOnline but that alarm never showed up so the Processor must have been responding to request.
I know that since the PLC was faulted it wasn't scanning the values for a change so that is why the HMI was stuck on a value that was "reasonable".
So how would you go about getting some kind of alarm on the HMI to let people know that the data they are looking at could be wrong?? Or how do I go about making forcing the tank levels to a really high value in the event of a Major Fault?
I need to find a way to try and keep this from happening again! I have other plans in place to also help but I cant have the HMI showing good data if the PLC isn't even working properly.
Thanks so much for any and all help!!