How to get an EDS file for Micrologix 1100?

strantor

Member
Join Date
Sep 2010
Location
katy tx
Posts
401
I want to talk to a micrologix 1100 from a Productivity 3000 PLC using Ethernet/IP protocol. I believe I need to generate an EDS for the Micrologix wherein I specify what memory areas are exchanged; at least, that's been the procedure with other PLCs. But I can't find any method of generating an EDS in RSLogix500. How do I get these two PLCs talking? I suppose I could do it the other way around (generate an EDS in Productivity Suite and import it into RSLinx) but I have reasons to prefer the other way.
 
What sort of EtherNet/IP connections does Productivity 3000 support ?

The MicroLogix 1100 and 1400 controllers do not support cyclic Class 1 I/O style connections or Produced/Consumed tags.

If the Productivity 3000 supports messaging using the A-B "PCCC" data table access protocol, then that's going to be your best way to connect the controllers.

MicroLogix 1400 supports Modbust/TCP as well, but the MicroLogix 1100 only supports Modbus RTU on the serial port.
 
Last edited:
If the Productivity 3000 supports messaging using the A-B "PCCC" data table access protocol, then that's going to be your best way to connect the controllers.

Sounds like they thought about supporting PCCC but not sure if they ever did

Page 40

PCCC (used for reading and writing values to Allen Bradley
MicroLogix and SLC PLCs) are planned for subsequent phases of this protocol.

https://cdn.automationdirect.com/static/manuals/p3userm/ch6.pdf
 

Similar Topics

Hey y'all!! I'm looking for an old EDS file, GSE 560. I can't find them anywhere. It is for a GSE560 display on a DeviceNet network, with...
Replies
0
Views
116
Hello, This product that I have the 1790D-T8BV8B is discontinued, does anyone have the EDS file for it? I wonder if TechConnect will have this...
Replies
8
Views
221
Hello Friends We have 10 Powerfocus 4000 with DeviceNet, We need to backup the configuration, the Powerfocus is detected but as unrecognized...
Replies
0
Views
126
Hi everyone: I went to AB.com, found only firmware, no EDs file showing up. i took a pix of device properties of RSLinx. Thanks
Replies
1
Views
148
Hi all. Please can anyone assist me with a Devicenet EDS File or link for a Numatics G2-2 solenoid valve bank. Need to do configuration on a...
Replies
3
Views
758
Back
Top Bottom