How to get rid of -- 17056 i.e. Group/axis consequential error in TWINCat System
Sep 2013
Pune
24
I am using TWINCat PLC to control two Rexroth Indra Drives (say drive A and drive B) via a virtual axis (say V).
Basically, B has to speed up and match the speed A. B is coupled to V by MC_GearInDyn and V is then coupled to A by MC_GearInVel. To stop B without stopping A, I decouple V from A and so it stops and then B follows that and stops and A remains rotating. This logic works most of the times, but I sometimes get an error in my Virtual Axis. Since it is not a real error, I have to shutdown whole machine in order to clear it. The error, as described in TWINCat Info System, is “17056 i.e. Group/axis consequential error”.
Can somebody help me with this?
Thanks in advance...
If you go into System Manager into each axis and clear the error (F8) in the online tab, will that reset the alarm without a power cycle?
Hey,
Thanks for the reply.
I tried doing that in several occasions of this error and that does resets the error but then suddenly the axis name fades, I mean the system manager window becomes inactive so I left with nothing but to restart.
Can you give me more details like when this error 17056 generates in system ?
I can post more detailed explanation from TWINCat Info System about the error detail, if you want.
Thanks,
Saurabh
17056 is a consequential error. You need to find the original error and fix it. Find the original error by monitor the errors/warnings/hints in the system manager. You may have to enable showing of the logger window.
A MC_Reset should reset the 17056 after the original MC or drive fault has been reset.
Hello, I need to create an automatic transfer panel that connects to the generator when the mains power is cut. I can draw up to 60kW and draw up...
94
Hi All, I'm keep getting double quotes in between selections rather than the beginning and the end. Here's the script and please help to find...
811
Hi all, I'm trying to visualize an array of type structure using Datagrid control. Im assigning the array to the Model property of the Datagrid...
664
Greeting experts! We have a new machine we just built. It is equipped with regenerative drives. The machine uses Beckhoff controls (PLC and...
1,089
hi every one am controling the hbs86h driver with s7-1200 plc the drive have the PEND+/PEND- which indicates that the stepper reached it's...
868