dear
i am using 2 controller rack of 4 slot.
0 slot using for controller SLC5/4
1 slot 1747 BSN
same configuration for the other controller rack
13 slot of remote I/O rack through 1747 ASB
0 slot using for 1747 ASB
1 to 12 slot using for Digital Input & Output
next 13 slot of remote expansion rack conecting with interconecting cable of allen bradley
all slot are using for analog and thromocouple modules.
my question is that how to configure all modules in the I/O configuration of the ladder file
and also how to configure G file of 1747 BSN module.
For true redundancy, use ControlLogix.
As I recall, the SLC (and PLC5) modules give you a backup processor. There is always one dedicated as primary and one dedicated as secondary - not swappable. As for programming, both controllers have the same program, just with different node addresses. There is a sequence on how to download a project to this setup.
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
96
Hi guys, in a redundant dh+ network consisting of one IO scanner (1747-ASB) having a combination of different IO modules in a 13 slot chassis...
3,513
Hi, I am building a SLC redundant system in which i have to make analogue output redundant. I am afraid that when the load will be shifted from...
2,486
what are the software options, optional packages and hardware to conect one workstation to slc 500 redundant plc
3,126
Hi, I know this sounds weird, but that's exactly what we are looking for. Redundant Power Supply for SLC 500! Our scenario is that we have...
11,704