we are going to be integrating a new set of controls using the direct logic 205 platform. Please, i need some help in selecting a good, reliable humidity sensor which is compatible. Analog preffered.
need something under $400 preferably with a +-5%.
What kind of humidity? Relative humidity (RH)? Dewpoint? absolute humidity?
There are HVAC relative humidity sensors for well less than $400. Dewpoint is usually twice that or more. In a nutshell, RH varies drastically with temperature, Dewpoint varies drastically with pressure.
Industrial RH is typically higher temperature rated and somewhat easier to calibrate, since a lot of industrial RH needs periodic calibration, whereas HVAC is installed and forgotten.
I use Rotronics, F series for HVAC, hygroclip for industrial RH. If it's EXP, then Honeywell. Honeywell dewpoint is a no-no (doesn't work).
Everything I've used is 2 wire, loop powered with an external 24Vdc power supply.
Dan
Hello, I am writing my thesis for a company and I have to connect a GEFRAN H5000 humidity sensor to a B&R PLC. The information of the sensor...
7,722
Hello, I have Vaisala humidity and temperature transmitter HMD60Y. Do I need signal amplifier in order to communicate with Anolog to Digital PLC...
2,439
I am looking for temperature/humidity sensor recommendations. Would like the sensor to display temp and humidity. Need to connect to a Contrologix...
230
For you instrument people. I'm using a PLC, VFD, and HMI for climate monitoring and control. Automation direct has combo Humidity and Temp sensor...
2,014
so I have this (temp +relative humidity) sensor ( pfmini72) from mitchell instruments , the sensor works fine for temperature reading but when it...
5,956