I paid alot to learn that lesson. The HMI or most SCADA packaged momentary push buttons write a 1 followed a moment later by a zero. Or vice versa... The network if TCP is not deterministic which bit arrives first. If tthose two bits arrive in the wrong order, you get a stuck in pressed button on your display. Never use those HMI momentary PBs without adding in the PLC logic to unlatch the bit. I prefer an off delay timer, but there are lots of options. A simple network may never suffer the issue, explaining why some people never experience the issue.
I paid alot to learn that lesson. The HMI or most SCADA packaged momentary push buttons write a 1 followed a moment later by a zero. Or vice versa... The network if TCP is not deterministic which bit arrives first. If tthose two bits arrive in the wrong order, you get a stuck in pressed button on your display. Never use those HMI momentary PBs without adding in the PLC logic to unlatch the bit. I prefer an off delay timer, but there are lots of options. A simple network may never suffer the issue, explaining why some people never experience the issue.