I/P Valve PID Control
wanher3
Feb 2018
USA
65
Hello,
Would anyone have a tutorial or a good example of programing a PID controller for a I/P valve positioner ?
Are you talking about the internal PID in a 'smart' valve positioner that calculates the output response of the valve positioner, or are you talking about the PID control in a controller (using some process variable like pressure or flow) that generates a 4-20mA output that becomes the Process Variable/demand valve position signal that is transmitted to a valve positioner?
I am referring to the PID Control in a controller using pressure PV.
Please elaborate
"Pressure" is not enough information.
Good news depending on what the Pressure sensor is, what the measured media is, (hydraulic, pneumatic, other), and how responsive the control valve is... pressure is generally easier than temperature loops with long thermal lag times.
Most of our pressure loops work well with simple PI loops.
Plastic
The valve's positioner should essentially be "transparent". The controller's PID output is telling the valve where it should be to achieve a pressure setpoint. More open or less open (more closed) or hold.
The PI tuning constants for the couple apps I was involved with had low gain (large proportional band) and a low amount of reset with no rate action at all.
But the values always depend on the system dynamics.
@wanher3
It would help people to help you if you described the situation better.
What are you actually controlling with the output of the PID (Pressure or Position for example)?
What is your desired outcome (force or Position)?
What is your feedback for the control loop? (pressure, force, position?)
consider drawing a sketch.
Nick
Hi All, Has anyone any experience in controlling a non linear valve with a PID? Traditionally this valve is controlled on flow but would like to...
36
11,023
Second guessing myself here, need someone to either tell me I'm wrong or confirm that my thinking is correct please. I have an equal-percentage...
2,745
Hi guys, Need some help. Goal: Closed loop flow control of valve positioner to a flow value. Parts: I've got a K series Rotork valve with...
4,267
Good Morning, This may be an easy question for some...but I'll need a little guidance. I have a project where under a particular condition I...
1,609
Hi guys. I work mostly with AB products and have been given the task of adding a PID block to a GE 90-30 plc to control an analog output based...
32,234