IAI PCON-CB EtherNet/IP Controller to Studio 5000 Invalid Input Size

irinjia

Lifetime Supporting Member
Join Date
Jun 2017
Location
Ireland
Posts
7
Hi All,

Can I get help with the following Invalid Input Size Fault displayed in Studio 5000.

Allen Bradley:

Studio 5000 V33
CompactLogix L306ERM

IAI Corporation:

Model: PCON-CB-35PWAI-EP-0-0-DN
Actuator: RCP6-SA4C-WA-35P-10-400-P3-P

Please see attached PDF with more details.

Thank you.
 
Hi All,

I resolved this issue using PC Interface Software for RC/EC.
Changed paramter 84 to 3.

Thanks for reading and this might help someone in future.
 