ICOM to RS5000 conversion
HAROLD
Apr 2007
St Catharines
I found in my archive an old PLC5/11 program that was created using ICOM software which I no longer have access to. Is there any way I can import it to RS5000 or is my only option to upload from the functioning PLC and work without the benefit of comments and such?
Thanks for any input
There is a "conversion" utility that comes with RSLogix 5000 that will convert about 80% of the ladder code from a PLC-5 into an RSLogix 5000 format. I don't think it qualifies as "import", but it's a lot better than typing by hand.
This utility requires an exported ladder file and an exported description file from 6200-PLC5, AI-5 or RSLogix 5 software.
Any A-B distributor can do this for you, as can RA Technical Support. Forum users are generally happy to assist as well; many of us have PLC software that we still use for exactly this sort of thing.
Thanks Eddie
I found a translate utility but it looks for a .txt file that doesnt exist.
Before we get too caried away can you tell me if what I found is in fact what I think it is.
Some of the larger files in my folder have extensions: .DSI .DSC .ADR .CFG .X5 .SYM
Are these in fact ICOM type files and do I need the ICOM software to create the export file that RS logix 5000 is looking for.
Harold
RSLogix5 should be able to open the .X5 file you have. The other files are needed too, but that is the main one that the software looks for.
Once you have it in RSLogix5, you can save it out as the .PC5 file that RSLogix5000 wants to translate.
BTW, AI-5 is ICOM for the PLC5.
Those sound like the right ICOM extension.
If you don't have RSLogix-5 then zip the files and post it. Someone here can convert it to a PC5 file for you.
Hi folks ! Got an older Modicom BM85 and I suspect that it's not passing data to ModBus+ network. We had a power loss for a few days and I suspect...
70
We're upgrading an old PLC-2 system programmed in ICOM. We have the files, the PLC logic is in a .LAD format. Does anyone have working...
428
Hello expert I have migrate legacy project that use Applicom OPC DA with 3rd client and S7-400. I see in client code add item string call...
375
We have Wonderware 2012 all set up (been set for years) using a server in the SMC console this can be seen as DASAPPLICON to talk to an S7-400...
1,054
Trying to use the APPICOM OPC server that comes with Bradcommunications APPLICOM Card for wornderware. When I "browse" the OPC tags I get Group...
4,333