IEEE 64bit floating point
jdpenrod
Feb 2006
Houston, Texas
does anyone have an example on how to convert a double precision (64bit) floating point number to single precision in a SLC500. i am polling an "accuload" with modbus and populating four integer files that make up the dp number. how do i get it to sp fp?
It can be done - but I have never done it and though I wish I had the time to tinker with it now, I don't.
If you aren't familiar with the floating point format used in the SLC, see this AB technote first:
http://domino.automation.rockwell.com/applications/kb/RAKB.nsf/0/85C2838CBFC456D285256AFB00695031?OpenDocument
Here is a really cool utility that lets you see exactly how a floating point number is represented in binary.
http://babbage.cs.qc.edu/courses/cs341/IEEE-754.html
http://en.wikipedia.org/wiki/IEEE_floating-point_standard
I started thinking about how to do this after work and so this is what I banged out.
I tested it on a SLC5/05 and it seems to work OK for numbers such as PI, 999.99, 3.402823466E+38, 2, and 0. I think it will work for all double floats that are in the valid number range for a single float. If the number is bigger than 3.4032823E38 then this is not going to work - it will return infinity.
There is probably a better way to do it - but it appears to work. At least you can see how to do it.
This routine truncates the mantissa at 23 bits, IT DOES NOT ROUND.
Use it at your own risk - no warranty to accuracy is made.
Make sure you get your words in the right order into N207:0 thru N207:3.
(note: Ignore Rung 31. It was there for testing and it doesn't do anything for the conversion. I forgot to take it out before making the PDF and I'm too tired to redo it).
I had another thought on this particular problem. This is a simpler but more limited solution.
If you are absolutely sure that your double will not have an exponent larger than 38 or smaller than -38 then you can make it really simple.
Just map the bits from a 64 bit field to a 32 bit field (two consecutive integers) as shown and then use COP to move the two integers to a float. This doesnt provide any range checking but it is simple to do.
63 -> 31
62 -> 30
61 -> ignore
60 -> ignore
59 -> ignore
58 -> 29
57 -> 28
56 -> 27
55 -> 26
54 -> 25
53 -> 24
52 -> 23
51 -> 22
50 -> 21
49 -> 20
48 -> 19
47 -> 18
46 -> 17
45 -> 16
44 -> 15
43 -> 14
42 -> 13
41 -> 12
40 -> 11
39 -> 10
38 -> 9
37 -> 8
36 -> 7
35 -> 6
34 -> 5
33 -> 4
32 -> 3
31 -> 2
30 -> 1
29 -> 0
28 -> ignore
27 -> ignore
26 -> ignore
25 -> ignore
24 -> ignore
23 -> ignore
22 -> ignore
21 -> ignore
20 -> ignore
19 -> ignore
18 -> ignore
17 -> ignore
16 -> ignore
15 -> ignore
14 -> ignore
13 -> ignore
12 -> ignore
11 -> ignore
10 -> ignore
9 -> ignore
8 -> ignore
7 -> ignore
6 -> ignore
5 -> ignore
4 -> ignore
3 -> ignore
2 -> ignore
1 -> ignore
0 -> ignore
Looking for some explanation/history between North American electrical symbols standards (how they relate, what are the latest, what is the...
1,721
Hello! Long time lurker and gatherer of information - love this forum. I am trying to find some sort of tag naming standard if it exists...
18
8,420
Dear friends across the pond, Does anyone know which one is the IEEE standard regarding the harmonics performance of the VSDs? Regards Nik
2,116
OK, so I have a ControlLogix L61 Processor and I am communicating with a Veeder-Root 350+. I have established the comm and am getting valid data...
5,544