I'm a idiot how to scale!!
jasil
Jun 2012
Building
48
I'm confused SLC500 is fine I understand, but Controllogix 5000 revision 20.
1756 IFHI8 card how do I scale the input? The input is a dumb analog device 4-20ma and I can obviously change the high engineering and low engineering units, but where can I see the raw data?
The transducer isn't ever outputting a true 4ma my guess would be 8ma with a high range of maybe 15ma. Where can I see the raw data to scale it accordingly?
I've got that lol............how do I know the real MA input to the card though? That's just the range why can't I actually see the MA range in realtime, so I can scale accordingly.
I could put the engineering units at whatever I want, but the transducer will never hit the 4ma nor will it ever hit 20ma, so the scaled input range might be 7.65ma min and 17.37 max?
Make sense or no? How can I look at the card and get those min and max levels by moving a field device?
A VOM connected in series set to the milliamp scale comes to mind...
I agree I was hoping in this age and seeing that it is Controllogix it would show the raw input data. If a SLC shows it why doesn't the array of HART cards now used by AB?
Yes, that is the last resort.
have you looked at the local input tags?
You just made the light bulb come on. Couldn't I just put the High and Low engineering units at 4ma and 20ma and see what the channel data is at that point? That would give me a accurate reading, at least I think it would.
normally I do put the high and low units at 4 and 20.. send a signal and figure the scale. not figure but setup the scaling.
See attached file.
A picture is worth than 1000 words.
You can use 4000 and 20000 for raw engineering instead of enegineering units.
Then you can use 4000-20000 range as your input for a block scale or AOI instruction.
Here is another way to do the scaling so that you can see the raw counts and the ma readings. You set your analog card's comm format to integer data then using the function block programming scale the raw data for your deivce, it seem to work well.
Last resort? If you aren't sure about what your transmitter is putting out compared to what the PLC is reading, this would be my first stop.
The CLX will show the raw data, at the most you have to create a tag and load it in.
We scale ours here to 30840 (upper end obviously) to give us some head room in case there is a transmitter failure (which then would pump out 22 ma). So anything substantially above 30840 would indicate that there was a problem with the transmitter.
Maybe I didn't fully understand the question. :unsure:
And what's this about HART?
How do I? "LVA_SW1_SPD_REMOTE" "LVB_SW1_SPD_REMOTE" JC If first line is =1 or second line =1 Jump _003: \used to stl
1,374
If you were going to go down to the closest overpass or homeless shelter to hand pick a person to install, program, and tune 1/16DIN panel PID...
5,792
Please... for the love of all that is good and evil, help me understand how to program a simple analog program! I have a 10 ohm potentiometer...
27
9,932
Hi all I'm trying to setup a very basic "live map" of a bussiness park (nothing as fancy as what you guys normally do :)). It is basically a...
1,428
Hi all, I have spent about 3 days after hours searching around the net and I have picked up enough information to order a 3kW 8 pole for an AC...
30
10,032