input debouncing
oldNovice
May 2005
San Jose, California
I have been away from this site for some time because I have been consumed with programming my SoftLogix5000 for my SoftLogix5800 controller.
I am now in need of some help! I need the ladder logic for a input debouncer for both ON and OFF debounce, each with either the same or different filter times (~ 400 mS to 550 mS).
I would appreciate any help on this!
Thanks,
oldNovice
I'm not familiar with SoftLogix, but here's an example of debounce logic...
| INPUT +----------+
|----] [---------------| TIM 1 |
| | 0.4 sec. | ON-DELAY
| INPUT +----------+
|----]/[---------------| TIM 2 |
| | 0.3 sec. | OFF-DELAY
| TIM 1 TIM 2
|----] [---+---]/[---------( OUT ) DEBOUNCED BIT
| OUT |
-Eric
Eric,
Thanks! You made my day. I was going the wrong direction simply because I was relying on my old microcontroller assembly programming and started out with an XOR of the current state versus the present state. It worked, to some degree, but was getting way out of hand with logic.
Thanks,
oldNovice
363
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
30
1,143
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
259
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
119
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
88