Hi guys,
I installed a Bindicator on our dust collector to indicate when it plugs up. I have it all mapped correctly to a P_DIN Block in RSLogic5000. I have the tag connected to Inp_PV of the block and when I change the state of the device the state at the Inp_PV changes from a 1 to a 0 which is normal. When I open up and view block properties and check watch the Inp_PV nothing is changing. It's seems like I don't have the block enabled so the input connected to it has no effects on the block internally.
Any ideas?
Gus
just guessing - but it sounds like you're not scanning/executing the section of code where you've placed this instruction ...
if the code is located in a SUB-routine, then you probably need to install a JSR instruction located in the same program's MAIN-routine ...
on the other hand ...
if the code is in a brand new routine - in a brand new program, then the routine probably needs to have a little "1" badge on it ... in that case, the following link might be helpful ...
http://www.plctalk.net/qanda/showthread.php?p=567395&postcount=9
if none of this helps, then you might want to consider posting your ACD project file (you'll have to zip it first) ... personally I've never heard of the type of instruction that you've mentioned ... maybe this is an Add-On Instruction ???
Thanks Ron,
I wasn't the one that initially installed the control Block so I just assumed a JSR was created. I didn't think to check there until you pointed that out to me. I just added a JSR on the main routine page for the tag I was working on and everything is working great.
Awesome support!!!!
369
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
30
1,145
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
259
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
119
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
88