The only argument I can see is that if they loose the prints they have something to halfway go by.
If they loose the prints, well then, they don't deserve to be fed!
We use Sheet number/Column Number/Sequence Number method for 90% of our drawings - most of the time we are building new panels from scratch.
This means that every wire number is a minimum of 3 characters - Wire number 732 would be found on Sheet 7, Column 3 and then sequence 2 (assuming that there is a wire number 731 above it).
We have also used the Instrument tag method on larger jobs - eg Temperature Transmitter TT100 might have the wirenumbers TT100-1 and TT100-2 if it is 4-20mA loop, or TT100-1, TT100-2 & TT100-3 if it is a RTD... this method works well with compact/contrologix systems where you can use tag based addressing - not much help if you are using a different PLC IMHO, as you cannot find easily where TT100 connects to the PLC