Prayder Lifetime Supporting Member P Join Date Jun 2014 Location Arkansas Posts 254 Jan 5, 2015 #1 Getting message that says mode or state of module does not allow object to perform requested service. Things to check?
Getting message that says mode or state of module does not allow object to perform requested service. Things to check?
Bolatov Member B Join Date Jun 2010 Location Mty Posts 87 Jan 5, 2015 #2 Loosen connections on the bus duplicated address check the chasis size in the project I/O Tree properties of the module
Loosen connections on the bus duplicated address check the chasis size in the project I/O Tree properties of the module
Prayder Lifetime Supporting Member OP P Join Date Jun 2014 Location Arkansas Posts 254 Jan 5, 2015 #3 Yep... spot on. It was the chassis size in the I/O module.. Thank you!!