Hi everybody,
I’m trying to find the best way to do invert a 4-20 mA signal in the device, PLC and citect.
I have a Rotork actuator which open and closes a weir gate. 0% is fully closed and 100% is fully open. I just want to invert this process so it’s easy to understand for the operators.
0% = Opened and 100% Closed.
I have found the invert option in the instrument panel for the actuator, whats the best way to tackle this in the processor and Citect.
Any help will be much appreciated
Thank you
Ov = [(Osh – Osl) * (Iv - Isl) / (Ish – Isl)] + Osl
Ov = scaled output value
Iv = analog #Input value
Osh = high limit of the scale for the scaled Output value
Osl = low limit of the scale for the scaled Output value
Ish = high limit of the scale for the Input value
Isl = low limit of the scale for the Input value
If you decide to invert the signal in the PLC you are better using the full scale formula rather than the short version, because it assumes you have the lower value at zero. The formula above will scale anything to anything and still works if you go outside the maximums and minimums.
Use BryanG's formula to calculate the 4 to 20 value. Then subtract that value from 24.
24-20=4
24-16=8
24-12=12
24-8=16
24-4=20
You don't even have to do the extra maths, just make the output high limit 4 and the low limit 20. It will do the inversion for you. Have no experience with Kingfisher RTU.
I find that what 0%=close, 100%=open is what operators expect. 100%=closed 0% open is opposite of most controls and confuses the operators and electricians.
But how do i make the change in citect? i don't think i can have 100% low limit and 0% high limit.
I agree. I also suggest documenting it somewhere that would be found if they were trying to troubleshoot a problem.
Will.
l suppose if you are more interested in the valve being closed, 100% would be a good percentage, but has been suggested 100% is normal talked about in open.
But in thinking about what you suggest, 100% closed would be a better figure as that is the safest position for a lot of processors.
Turned off, is normally the safest position.
But when it gets hooked up to a HMI and showing graphics, 100% on a valve would show full throttle (open) when looking, not unlike 100% on the throttle when in a car spinning the wheels, not 0% on the throttle spinning the wheels.
Hi, Has anyone had this problem: - I send a speed reference to my ABB ACS550 Drive via Modbus TCP to it's register via an INT. However when I...
1,017
Converting an iFix 5.0 HMI to Ignition, not developed by me. Been a long time since using iFix. On Digital Input tags, what does the property...
1,889
A B D E G ---| |----| / |---+---| / |---| |------+----( )--- | |...
2,184
how to Invert the Analog water Level Sensor values? It messure number in int from 27565 (tank empty) to 0 (tank Full) It there som kind of...
6,213
Good evening everyone (or good morning) I am writing a program that has a analog input, I have scaled it to my 0-10v and its working great...
4,838