Is my embedded analog input broken?
turner15429
Apr 2018
Landrum, SC
I'm having issues collecting a readout from my analog input. The signal is 4-20 and it is coming from a signal conditioner that conditions a load cell input. I have a tag that has the alias Local:2:I.Ch2Data(C) that gets scaled with SCP. when I enable the input and monitor it it slowly goes up. If I disable and re-enable it goes slightly down and begins counting up again. I have my dc+ connected to I 2+ and dc- to V/I in 2- My analog outputs are working great. any feedback is appreciated!
The analog input has an internal 249 ohm resistor (assuming a rockwell plc) so 4 ma = 1V across the terminals, 20 ma = 5V across the terminals. So you can check whether the signal into your analog channel is working or is somehow gradually counting up.
Getting ready to build a machine and use a Allen Bradley Compact Logix 1769-l24er-qbfc1b It has a embedded HSC and Analog. Using the HSC on a...
1,816
I have a new Micrologix 1400. I have an SCP instruction that should give me a 0-4095 output on O:0.5 address. Problem is it does not ever change...
2,855
The Micrologix Programmable Controllers - Instruction Set Reference Manual describes analog input data files for two different modules and analog...
16,006
Hello everyone! This is my first time posting, though I have been to this site a few times hunting for some random problem like we all do. I...
190
Hi Guys, I have a 1769-L24-QBFCB1 that has the OK light flashing on the embedded counter module. The manual states it is a resettable fault, but...
118