issue with PLC on multiple networks
DaleAlanB
Aug 2010
Pacific, Missouri
I have an AutomationDirect DL06 PLC (PLC A) that is presently a master on a multi-node RS485/422 network (network 1) using the on-board port 2. I am trying to attach this PLC to a second network (network 2) as a slave using port 2 of a D0-DCM module. Network 2 will not always be active which is why I'd like PLC A to be a slave on network 2.
The problem I am having is when I attempt to start network 2, the red error light on the D0-DCM module flashes along with the green TX/RX lights. And no data appears to transfer between PLC A and PLC B (master) on network 2.
If I rework my programs so the PLC A is the master on both networks, the error light goes out, and communication on network 2 is successful. So I know I have the D0-DCM configured correctly.
What am I doing wrong? Why can't I make PLC A a slave on network 2? It seems to me that I should be able to do this as long as I use a different port for each network.
I'm using DirectNet protocol on both networks. All PLCs are DL06. Each PLC has been assigned unique station numbers, and both ports on PLC A have unique numbers (I've also tried assigning the same number to both ports - port 2 on the on-board and the D0-DCM module - with same results). Both networks are serial. Network 2 will only have two PLCs on it - PLC A and PLC B)
Any help would be appreciated.
Thanks.
Post some of your logic, so we can look at it and assist with troubleshooting. I don't see any reason why you should not be able to do what you are trying to do.
Right off hand I think this is where the problem is (configuration)
Can you post your configuration?
JBJennings, milldrone, Thanks in advance for your help.
Here is the configuration I'm using. The D0-DCM is in slot 3 of the slave PLC (PLC A in original posting) [third slot from left]. On both PLCs I am using the GX/GY Global (Remote) I/O contacts as my network Input/Output area. I don't use these contacts for anything else.
I have DirectSoft 4 so I have to code the D0-DCM configuration within the program.
Note: The D0-DCM port configuration screens are only in DirectSoft 5.
STR SP0
LD K22E1
OUT V722
LD K4509
OUT V723
LD K55
OUT V727
On first scan:
Per the D0-DCM manual: The above should translate as: Auto Detect Protocol, Hex Mode,
RTS On: 2ms, RTS off 5ms, Base Timeout x 1.5, RS422/485 4-wire/RS232
Station Address 9, 9600 baud, odd parity, 8 data bits, 1 stop bit
Master PLC (PLC B) is using On-Board port 2 configured as follows:
Protocol: Directnet
Base Timeout x 1.5
RTS On: 5ms
RTS off: 2ms
Station: 8
Baud: 9600
Stop bit: 1
Parity: odd
Format: Hex
Master PLC (PLC B) RX/TX code.
STRN SP116
ANDN C700
LD KF209
LD K4
LDA O40000
RX GY220
SET C700
Read 4 bytes from GY220 on slave store at GX0 on master
STRN SP116
AND C700
LD KF209
LD K4
LDA O40200
WX GX400
RST C700
Write 4 bytes from GY0 on master store at GX400 on slave
Dale,
I cannot find anything wrong with the configuration. I'm presuming you have verified that the Vmems contain the values in you wrote in the ladder.
I have created a project in TIA Portal v16 Upd6 with S7-1200 (6ES7214-1AG40-0XB0) and WinCC Unified (PC station). The communication between the...
146
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
157
I am working on a project using a NB screen and NX1P2 PLC. I am having a really hard time getting a real number to properly translate through to...
121
We have a problem where client wrongly install inverters in their residence, this then prevents the elec meters(Hexing hxp100Dii) from...
88
Hi , Looking for some help. We have a 343-1 PN Lean Card & 315-2DP connected to an external system collecting data. After a recent shutdown...
69