Hi all,
I have a configuration of 4 kinetix 5500:
position 1 -> H025 shared AC/DC
position 2 -> H025 shared DC
position 3 -> H008 shared DC
position 4 -> H008 shared DC
randomly the drive 1 and 4 go in precharge state (1-2 times per week).
To exit this precharge state at the beginning i made a run/program/run
transition on CPU.
Today i simply let the machine in manual, so after a timeout the enable bit of the drives goes down.
At this point the drives exit the precharge and go in stopped state.
When the enable bit goes on again the drive goes in running and operate correctly.
Did you experienced something similar?
Thanks to all
Bartech
If you can, have a look at this RA Knowledgebase article for some pointers...
626724 - Kinetix 5500 Drive: Stuck in Precharge with Main AC applied
Access Level: TechConnect
Regards,
George
Unfortunately I don't have access to TechConnect. Today I opened a service ticket with Rockwell.
They opened my mind on a few points.
It seems that my ladder sequence is wrong.
I probably have to put a delay between the drive enable and the positioning request. Rockwell technician also says the drive should not go precharge.
I will keep you informed
thanks again!
Bartech
thanks again!
Bartech
Hi, can you share the ticket number, and if you solved this issue please?
Have same issue with going into pre-charge also DC Bus Voltage is showing 550V.
Thanks.
Hi all, I am upgrading a couple of 2094-BC01-M01 servos with 2198-H015-ERS. The original code uses MSG instructions to control (release, engage...
90
Hello everybody, I have Kinetix 5500 (2198-H040-ERS). I'm having issue with this drive. (I believe it's the drive/Kinetix and need confirmation)...
65
Good day: I am wondering if anyone has experience with the Kinetix 5500 S33 Fault. I have 3 drives in a group set as follows: 2198-H025-ERS2...
196
Hi guys! I have 3 servos for X,Y,Z axis controlled by Kinetix 5500. In Studio 5000 there is one Predefined tag in AXIS_CIP_DRIVE called...
207
Hi all, New here and new all round to PLC`s. We have a servo drive that runs a cross travel beam backwards and forwards. I am having trouble with...
259