Kinetix drive axis removed
Kataeb
Jan 2007
www.livelovelebanon.com
636
a Rockwell Kinetix 7000 drive and motor are actually removed from a machine. the project was engineered with RSLogix 5000 using motion axis control through Sercos interface 1756-M16SE. the fiber optic ring is closed again without the presence of the above drive.
what is the simplest practical way to run the machine again without any faults?
i was considering the Inhibit Axis feature, to avoid destroying the software.
any recommendations from the experts?
But RSL5000 will report it can't talk to the axis. Inhibiting the drive means the software has to talk to the drive to inhibit. If the drive doesn't physically exist, how will the s/w talk to it? Of course, I'm thinking of the case of removing the drive out of the project.
Or just try it without making changes to s/w. The PLC will blink the I/O indicating that there is a problem. then address all faults.
I remember reading a RA knowledge base article on how to temporarily disable / remove an axis without removing the software
It is something like
1) Take the Axis out of the motion group
2) disable or remove the SERCOS address from the M16SE
You may have to make changes to the software if it is directly looking at the axis for start permissives
i deleted the Kinetix 7000 drive from the Sercos network, the axis is now associated to none, and bypassed all program instructions related to the axis. download to the plc was successful, all red leds were gone.
but now i have flashing green leds on the Sercos interface 1756-M16SE. should i do any special settings or configuration to fix this? does any other module or drive require it?
i checked the online properties of the Sercos interface 1756-M16SE , its Internal State is "Program Mode".
what does this mean? what should i do? i am new to this...
The solution was to check loose cables and connectors on the motors and drives, straighten bent connector pins, … (machine assembly was done too fast!). It seems that the sercos network does not do his first run, until all drives have started properly one after the other!
I have a customer with a Kinetix 350 servo drive. They were having issues with the old servo motor so they replaced the servo motor with a new...
18
8,370
Hello all, I am having a problem that i have been struggling with. I have a kinetix 5700 dual axis drive and one of the axis on the drive remains...
2,814
Hi, Again, a topic about Kinetix 5100 servo drives. The controller is L33ER. The servo drive are 2198-E1020-ERS with a TLP-115-200-DJMC2A. There...
555
I am looking to upgrade some of our old Servo Drives to the newer kinetix 5700 style. currently we have 4 1394 axis that are all driven by 5kw...
887
Kindly, we have one Kinetix drive in stock, sitting since three years. Can we directly install and run it on the machine? Or it needs some...
2,589