Hello all,
Everyone was so helpful with my data encryption question several months ago, but now for a new question:
An integrator that I am working with has a pair of Koyo Direct Logic 405 PLCs. He is connected via Com Port 1 on the CPU to a serial radio. The problem is that the port keeps locking up after about 3 to 5 TX & RX. He has replaced the radios from Genas?(sp) to MDS Transnets with no change. The radios have been configured for 9600 baud and 8 data bits, Odd parity and stop bit 1. As I have stated before, I'm a radio guy so I may not know some of the additional details you guys may need to help me out, but I can find out! Thanks again for your help with my last question!
Chuck
 
Do the PLC's have the latest firmware? How about surge supression on the lines between the PLC and radio modem? Sometimes keying up the radio will induce voltage spikes on the coms line.
 
Check to make sure you have the RTS On and RTS Off delays set correctly in the PLCs. When you transmit through a radio, it takes a certain amount of time for the radios to sync up.

Here is a link for setting the RTS On and Off delays -
http://support.automationdirect.com/docs/comportsetup/

I have been using an RTS On delay of 50mS and RTS Off delay of 20mS.
 
Hey everybody,
Thanks for your responses, he figured it out. He was using DirectNet and apparently it is similair to Modbus as far as it needs to have "Buffering On" in the radio!
Thanks!
Chuck
 

Similar Topics

can some one help with configure the 2 port for communicating , i understood that i got to define a master slave relation but dont realy knows how...
Replies
5
Views
3,038
I need this screen creator for GC-53 software to get an program from GC-53 MHI KOYO , Please help me.
Replies
0
Views
105
I have a c-more micro with a three digit input box on one of the screens. This is being written to a memory location in a DL05. I don't have the...
Replies
3
Views
116
Hey, I am entirely new to PLC's and am trying to help my friend with a project. He wants to take the signal from a PNP photoelectric sensor as...
Replies
12
Views
2,242
I have an OPC Server (Kep) pulling tags from an AB 1769-L36ERM and a few different Koyo PLCs (450, 454). On the HMI (FTV SE) there's one screen...
Replies
4
Views
1,490
Back
Top Bottom